    Suction riser
    What are suction risers. What are their use for
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #2

    Jul 24, 2007, 09:11 PM
    Well if you are referring to refrigeration suction lines used as risers then they would be vertical pipes used to return the refrigerant and oil back to the compressor, some times when a compressor is located higher then the evaporator, returning oil is as important as returning the refrigerant thus the pipes are sized to maintain velocity while also trapping the oil at the base of the riser, this type of design uses two pipes in the rise(one smaller then the other to maintain velocity) Once the trap fills with oil, the higher velocity pulls it up the pipe to the compressor. Hope this is what you were referring to. Mike
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #3

    Jul 26, 2007, 07:03 PM
    Check with your equipment manufacture, many of them no longer approve suction line traps. Slope your suction line towards the condensing unit and depending on how high the vertical pipe is and refrigerant being used and the application, they may recommend decreasing the vertical line to a smaller size to keep the velocity higher. If you have two compressors operating with one common suction line make sure you size it correctly. Lack of oil is a compressor killer...
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #4

    Jul 26, 2007, 09:29 PM
    The double riser on the suction line is a standard in the industry for more then fifty years , the smaller line is untrapped while the other line is the same size and trapped, by trapping the larger line the oil will fill the trap causing the refrigerant to go through the smaller line thus increasing the velocity and then start pulling the oil from the trap , only one pipe is smaller and the other pipe that is trapped is the same size as the rest of the suction line.
    The use of oil traps in certain installations are crucial to the longevity of the compressor, without the use of traps the oil would have a hard time getting back to the compressor, in larger commercial spilt systems using DX coils you will find a diagram showing the proper installation of oil traps in the installation instructions.
    What are suction risers ? And what are they used for ? Yes I think that was the question and I hope I have answered it .
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #5

    Jul 27, 2007, 10:58 AM
    Trane, Carrier and York no longer approve P-traps on suction lines. I just went through this with a new Trane 70 ton split unit. I always used double risers with P-traps for years but, it's no longer approved and will void the warranty with Trane. Decreasing the riser size will increase the velocity to provide sufficient oil return without trapping oil. Most old timers like myself, added extra oil to allow for what the traps will hold, unfortunately now there's not much pride or interest in doing the job correctly.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #6

    Jul 27, 2007, 01:27 PM
    That is not so in regards to oil traps ! They are still used and recommended by manufacturers, reducing the size of a suction line to increase velocity is a poor way to return oil , can cause a constant restriction in the low side of the system. Building maintaintenance personel who are not involved in the every day design and installation of commercial air conditioning systems are usually uninformed as to the proper methods of installation and design.
    Steve Jones's Avatar
    Steve Jones Posts: 1, Reputation: 1
    New Member
     
    #7

    Jan 14, 2010, 08:20 AM
    At what intervals should oil risers be installed?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Molding on stairs where the tread meets the riser? [ 3 Answers ]

July 8, 2007 Thank you Esquire1, Stairman and Glavine for your responses, but please let me clarify. The staple marks are on the top side of the tread where it meets the riser, that is, they are on the part of the tread where you step when you go up and down the stairs. Your responses seemed...

Toilet suction [ 2 Answers ]

My toilet seems to have low suction when flushed. What can remedy this?

High pressure riser noises [ 1 Answers ]

Hi - I'm not a plumber, but if I describe the following can anyone offer suggestions: I live in a small block of flats in a two floor flat. My bedroom is on the top floor, just below the loft containing the cold water storage tanks. I believe these tanks serve about 10 flats. The high pressure...

Bent copper tubing riser [ 6 Answers ]

Hi all. We had a toilet leak in our upstairs bathroom. We've had a couple of plumbers out over the past couple of years to deal with the problem, but their work didn't fix the problem. As a result, our linoleum discolored and the floor got weak. We spent the day yesterday pulling up the...


View more questions Search