    My unit runs fine for a while and then suddenly stops.
    When it runs, I can measure 25VAC at the thermostat.
    When it stops, I have no 25VAC so I can not even run the fan in manual when it stops. After sitting for several hours, the system restarts and runs fine.

    I have checked the main electrical breakers, but it's fine.
    Also, when it runs, I added more freon to make sure that's not the problem.
    Air flow in the home is fine when it runs too.

    Seems like something with the control system. Any suggestions?
    I'm using a simple thermostat (mercury switches).
    If the compressor was overheating, would it turn off the 25VAC transformer power to the thermostat? Is the 25VAC the root cause or is something else causing the 25VAC to be turned off? What's most likely and what action is best to take?

    Thanks,
    Dave in SC

    Update: A friend looked at the unit and suggested that we clean the outside coils as they appeared to be dirty. He had some coil cleaning solution (seems to be NaOH - caustic soda from what I can tell). We sprayed it on there and let it sit for 5+min then rinsed with water. Repeated the cleaning and it seems to be much better. Upon turning the unit back on (we turned off the power before cleaning), I could feel an improvement in the air flow along the coils (placing hand on the coils). It ran all night without turning off.

    We looked at the cooling coils close to the blower unit.. . They were not freezing up and the water was running out of the case. Seems like that part is OK.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 3, 2006, 08:25 AM
    The control transformer should be on all the time. It may be defective and stop delivering voltage after it heats up. Or there can be a loose or broken wire, loose connection anywhere in the control wiring system.
    dave.croucher's Avatar
    dave.croucher Posts: 4, Reputation: 1
    New Member
     
    #3

    Jun 3, 2006, 10:33 PM
    Make sure your furnace filter is clean.I recommend the cheap ones as they let lots of airflow through.also most units have safety switches that will interrupt the 24v cicuit if the pressure gets too high or too low.cause:dirty coils,dirty filter,low on refridge.
    dodgeramit's Avatar
    dodgeramit Posts: 2, Reputation: 1
    New Member
     
    #4

    Jun 6, 2006, 05:36 AM
    New Update: The wiring terminal located inside the blower unit was very rusty. We eliminated the terminal by directly connecting the wires using wire nuts (following the same wiring connections that the wiring terminal was providing). Since this change, there have been no more problems. 24V is being provided all the time to the thermostat (I'd also checked those connections and all the screws are tight and the contacts were cleaned). So the root problem seems to be bad connections at the wiring terminal due to rust.:)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Looking for some people on the run. Big times [ 3 Answers ]

This person has 3 little onces and is pulling scam left to right and was told if she is caught she ain't going to live to tell just rumors. They need to be stop and put away for good. She runs with another female and 2 males. All I got is a cellular phone with her voice on it. She did me and...

How many times have you been sued? [ 4 Answers ]

Hello, I am hopping that someone can help me with this. I am trying to find out how many times a public company has been sued (e.g. Walmart, FCUK, McDonalds) Is there any website or place I can go to check into this fact? Thanks.

Round Trip times [ 4 Answers ]

My Question is if Series of Round trip times(RTT) is given.Then how can we find out The Smoothed RTT,The Deviation in RTT,The Time out interval at each value.

1993 Civic EX suddenly stops running and won't re-start [ 3 Answers ]

Hi all, My girlfriend's Honda Civic (1993 EX model) died within 3 blocks of her workplace the other day. Not being able to troubleshoot the problem in 5 deg weather, I towed it to my house to have a closer look. The car turns over just fine... the engine is not seized, the starter works fine...


View more questions Search