How to connect three phase city supply to generator!
Hi dear 'ask me' community,
I have a 30KW generator with a automatic transfer switch - it has a three phase input U, V, W and N which
Needs to be connected to the city power it then has an output that goes to the building. How do I know
Which phase of the city supply needs to go to the U, V, W and N (neutral). Can an incorrect phase
Connection cause damage to the generator - how can I avoid this!
Your help will be greatly appreciated!
Thanks - Maruli!
|
|
|
Uber Member
|
|
Aug 1, 2008, 10:33 AM
|
|
Please explain your experience with 3 phase.
I am not familiar with the code letters you refer to "U, V, W and N (neutral)".
Am I correct you are not located in the USA or Canada?
Are you familiar with a Phase Rotation instrument?
|
|
|
Uber Member
|
|
Aug 1, 2008, 10:38 AM
|
|
Use a phase sequence meter. Phase Rotation
Contact the transfer switch manufacturer. As long as the generator and the utility are providing power from the same phase you should be OK as long as the transfer switch doesn't detect phase reversal. Confirm with manufacturer.
|
|
|
Electrical & Lighting Expert
|
|
Aug 1, 2008, 01:16 PM
|
|
My opinion on this is that this is ABSOLUTELY NOT a DIY job. You should NOT be messing with this stuff, especially if you have to come to a DIY site to ask questions.
PLEASE call in a professional to do this job for you!
|
|
|
New Member
|
|
Aug 2, 2008, 11:31 PM
|
|
Originally Posted by tkrussell
Please explain your experience with 3 phase.
I am not familiar with the code letters you refer to "U, V, W and N (neutral)".
The generator is a Chinese product - looks like they are using German notation - what I can see from
the circuit diagram supplied, U=L1, V=L2, W=L3.
Am I correct you are not located in the USA or Canada?
Yes I am located in South Africa.
Are you familiar with a Phase Rotation instrument?
No - but I would presume it could tell be the 120 deg difference between the phases.
Thanks.:)
|
|
|
New Member
|
|
Aug 2, 2008, 11:36 PM
|
|
Originally Posted by KeepItSimpleStupid
Use a phase sequence meter. Phase Rotation
OK - will try to get hold of one!
Contact the transfer switch manufacturer. As long as the generator and the utility are providing power from the same phase you should be OK as long as the transfer switch doesn't detect phase reversal. Confirm with manufacturer.
Will check with manufacturer first.
Thanks for all your information - much appreciated!:)
|
|
|
New Member
|
|
Aug 2, 2008, 11:46 PM
|
|
Originally Posted by stanfortyman
My opinion on this is that this is ABSOLUTELY NOT a DIY job. You should NOT be messing with this stuff, especially if you have to come to a DIY site to ask questions.
Oh I did not know that this is a DIY site I thought I could ask any questions!:(
PLEASE call in a professional to do this job for you!
Being in Africa it's often the case that the professional can blow-up your equipment - so it's better
To research and know exactly what needs to be done yourself!:)
|
|
|
Uber Member
|
|
Aug 3, 2008, 04:58 AM
|
|
Ok.
Any generator system needs a transfer switch, either a manual unit or automatic.
This isolates the utility line from the generator output, so the load only connects to either the utility or the generator, and there is no chance of the gen power getting out into the utility lines.
Simply use a phase rotation instrument to check and note the rotation of utility lines and of the gen output at the transfer switch. If the gen output is different that the utility, simply switch any two wires of the gen output.
Now the load will be fed by either the genset or utility with matching rotation, or sequence, of phases.
|
|
|
Electrical & Lighting Expert
|
|
Aug 3, 2008, 06:22 AM
|
|
Originally Posted by maruli
Being in Africa it's often the case that the professional can blow-up your equipment - so it's better
to research and know exactly what needs to be done yourself!:)
Here is yet ANOTHER case of knowing your location FROM THE START would have been a BIG help. :rolleyes:
|
|
|
New Member
|
|
Aug 3, 2008, 09:56 PM
|
|
Originally Posted by tkrussell
Ok.
Any generator system needs a transfer switch, either a manual unit or automatic.
OK
This isolates the utility line from the generator output, so the load only connects to either the utility or the generator, and there is no chance of the gen power getting out into the utility lines.
OK
Simply use a phase rotation instrument to check and note the rotation of utility lines and of the gen output at the transfer switch. if the gen output is different that the utility, simply switch any two wires of the gen output.
OK I have read up on a phase rotation instrument, and I will be able to obtain one locally!
Now the load will be fed by either the genset or utility with matching rotation, or sequence, of phases.
Your information has helped me a great deal - thank you very much!! :) :) :)
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Three phase generator
[ 4 Answers ]
Dear Sir,
If a three phase generator is loaded more on one phase and less on other does it effects is performance. At times a phase on generator runs overload while the other runs underload. What is the way to distribute the load equally on the three phases ?
Please suggest.
Regards,
Nipun Jain
Running 220 single phase from generator?
[ 1 Answers ]
I recently bought a wood planer. The id plate on the motor tells me it is 3 hp wired 220 single phase. The planer plug has three prongs on it. I plan to use this in my shop. My shop is powered with a 7000 watt generator. My generator has 220v but it has a 4 prong plug. CAn I change the plug on...
View more questions