  1. Yes, I mean jumper the controls to bypass the...

    Yes, I mean jumper the controls to bypass the switch. I didn't see any moisture or oxidation on the board and tried the disconnect/reconnect. I'm getting the same result.
  2. Sorry for the late response, rain and travel... ...

    Sorry for the late response, rain and travel...

    OK, I was able to turn on the furnace from the service switch then jumper the end switch within about 5 seconds. I still hear the click and still...
  3. I closed it with a jumper wire. Now the LED is...

    I closed it with a jumper wire. Now the LED is flashing "3".
  4. I tested the end switch with the inducer on and...

    I tested the end switch with the inducer on and got a reading of infinity, so no continuity.

    There was another safety device. It's an auxiliary swicth attached the back of the blower and in a...
  5. I had previously removed the exterior side...

    I had previously removed the exterior side shields, chimney, extension and the entire vent motor. This is how I found the nest in the frist place. After cleaning it out, I was unable to see any more...
  6. Goodman Gas Furnace - LED flashing "2" error code

    I have a 5 year old Goodman PGB024075-1A gas furnace. The LED is flashing a "2" error code, meaning an open end switch. I'm attempting to track down the potential causes of this error. After taking...