Had similar condition with a Goodman gas furnace. Search for the thread called "blower on furnace is possessed".
Hope it helps you fix your problem.
-
I replaced the control board yesterday and the unit is working correctly again.
Thank you bkspero! Your advice was perfect. I picked up a new board on eBay and swapped it for the old one just as...
-
Do the voltage measuremnts above mean anything to anyone?
-
NorthernHeat,
I measured low voltage at thermostat. I left the system in the OFF/AUTO mode and the blower is still automatically cycling on and off.
When the blower is OFF:
Common+red=27V...
-
Thank you for offering me your great advice everyone.
NorthernHeat, I will make the voltage measurements to verify that the board is bad.
Thank you bkspero. The shut-off delay makes sense -...
-
My model number is GMP 075-4.
-
By the way, I don't see an adjustable limit switch.
-
Sorry about that, correct model number for gas furnace is GMP 075-4
(Fortunately) the problem occurs somewhat consistently. Blower motor is OFF for approx 5-10 minutes, then the blower turns ON by...
-
Thanks for your suggestions hvac1000.
I'd like to try and make the repairs myself. My furnace is a Goodman model 1026. It is about 10 years old.
I think I've been able to rule out any problems...
-
The blower on my Goodman gas furnace came on all by itself tonight? Every 5-10 minutes the blower turns on for approx 1 minute then turns off by itself. Then the cycle repeats.
I verified that the...
-
Had a similar problem...
House was very cold; could not maintain temperature.
Gas furnace would reach set point, shut off, and then not turn on again.
Only way to fire heater (Goodman) was...
-
|