I need to get power to my above ground pool it is approx.100 feet from the elecrical panel what size wire do I need and when I bury it does it need to be in conduit?

16 Answers
quadragin's Avatar
quadragin Posts: 3, Reputation: 1
New Member
 
#2

May 6, 2008, 09:34 PM
You can run direct bury romex, for that run I would use 10/2 with a ground.
Typical 20Amp circuit is 12/2 romex you might get away with 12/2 but above ground pool pumps are 110volt and pull large amps like in the 15 amp range.
You might want to run 12/3 and see if your pump will run on 220 about 4 amp draw.
By the way 12 = 12 gauge and the 2 = 2 wires.
You will also need to install a 20 amp GFCI Breaker, or get an outdoor GFI plug and box.

DO NOT RUN extension cords as you will burn up your pump.
Helpful
jack dandy's Avatar
jack dandy Posts: 227, Reputation: 52
Full Member
 
#3

May 7, 2008, 07:27 AM
I heard through an electrician I talked to after I had my pool installed that 220 is the better way to go as far as cost and wear and tear on your electric motor in the long run its better.
Helpful
tkrussell's Avatar
tkrussell Posts: 9,673, Reputation: 3698
Senior Electrical & Lighting Expert
 
#4

May 7, 2008, 02:05 PM


The advice you received regarding the cable is absolutely incorrect.

First off, Romex is never allowed to be buried. It cannot be in any wet location. Let alone in the ground.

There is a cable that looks like Romex, but is it called UF cable, and is allowed to be buried,

However,

UF cable is not allowed to be used for pool wiring either.

Most locations allow widely used Sch 40 PVC conduit, complete with all fittings , and pulled through THHN/THWN or XHHW wire.

Pool wiring is very critical. Best to contact your local electrical inspector. Each state and city can have their own specific requirements for pools, along with the National Electric Code.Many will have a detailed sketch showing exactly what is expected.

Use 240 volt rated motors if available. They don't run any more efficient, but the higher voltage will help with the voltage drop. The distance you have will require voltage calculations to be done, based on the voltage, HP of the motor, type of wire used, etc. Guessing here does not work.

I am the first to help a DIY'er, but with pools, there are many various requirements all changing with the wide differences of the situation.

Ground fault breakers, special grounding, locations of outlets and lighting, only to name a few.

Best to call in a pro on this.
Helpful  (1)
kenjr1960's Avatar
kenjr1960 Posts: 2, Reputation: 10
Junior Member
 
#5

Apr 8, 2010, 08:41 PM
I am installing a above ground pool about 250ft from my house, I know there is a voltage drop,motor is 115v and 12 amps, what size wire and gfci breaker should I use.
Helpful
tkrussell's Avatar
tkrussell Posts: 9,673, Reputation: 3698
Senior Electrical & Lighting Expert
 
#6

Apr 9, 2010, 02:47 AM


For the data provided , this motor will need #6 copper.

Better of using a 240 volt motor, same size would need #12 wire.
Helpful
kenjr1960's Avatar
kenjr1960 Posts: 2, Reputation: 10
Junior Member
 
#7

Apr 9, 2010, 06:11 AM
So, your saying 240 volt motor use #12 wire and 2 pole 20 amp gfci breaker. And at the motor I will have 240volts ?
Helpful
tkrussell's Avatar
tkrussell Posts: 9,673, Reputation: 3698
Senior Electrical & Lighting Expert
 
#8

Apr 9, 2010, 06:47 AM


Yes, but the motor will need to be rated and connected for 240 volts.

This assumes the motor will be 6 amps at 240 volts.

A 2 pole 240 Volt GFI circuit breaker will be needed.
Helpful
davesmth41's Avatar
davesmth41 Posts: 1, Reputation: 1
New Member
 
#9

May 16, 2010, 07:18 AM
I just got done doing this same thing, and the variance in code is crazy from town to town. I ran a new service cable 4-4 from the main panel to my shed where I installed a 100 amp sub panel (180 feet). Also be careful, our local home depot told me 18 inches buried was satisfactory where in reality I had to go 36 inches (rented trench digger for this $114 for the day). I then ran 12-3 UF in conduit from the shed sub panel to the pool power post (40ft). All cables had to have 5 ft of conduit going into/out of the ground. I did all the work, had an electrician verify and sign off my permit ($86) and make my connections. Inspector was thrilled and I am all done. All in all, about $700, service cable is not cheap.
Helpful
tjf101's Avatar
tjf101 Posts: 2, Reputation: 10
New Member
 
#10

Aug 3, 2010, 04:14 PM
If you use 240v instead of 120v it will cut the amount of amps the motor pulls in half, which in turn will lower your electric bill. I do not believe you need #6 for a 240' run. Voltage drop does not play much of a factor until you pass 300'.
Helpful

Not your question? Ask your question View similar questions

 
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Add your answer here.

Remove Text Formatting

Undo
Redo
 
Decrease Size
Increase Size
Bold
Italic
Underline
Align Left
Align Center
Align Right
Ordered List
Unordered List
Decrease Indent
Increase Indent
Insert Email Link
Wrap [QUOTE] tags around selected text
Wrap [CODE] tags around selected text
Wrap [HTML] tags around selected text
Wrap [PHP] tags around selected text
Wrap [YOUTUBE] tags around selected text
Notification Type:



Check out some similar questions!

Above ground pool in ground [ 5 Answers ]

Can I put an above ground pool in a hole with about one foot of it sticking up? What do I do about water splashing out and washing away the back fill? What do I do about pluming and elec.? Thanks

Above ground pool [ 1 Answers ]

How do I find where my pool is leaking?

Install New Pool Liner-Above Ground Pool [ 1 Answers ]

We are going to install a new liner in an above ground pool this weekend. I have read conflicting information as to when the skimmer and jet holes should be cut. Do you fill the pool with water within a foot of the skimmer, attach the trim kit and then cut out the liner? I don't know what to do,...

Above Ground Pool [ 1 Answers ]

I have a 20' above ground pool - approximately 4 years old. About 2 weeks ago I noticed that on 1 section of the liner, wrinkles have started to appear and that the liner itself bumps out a little more toward the top of the pool than in other sections. The wrinkles may have been there before, but I...