    Bathroom Venting Scenarios
    Hello, After reading a few hundred posts and still not knowing what to do for sure I guess I'll have to ask speedball his millionth basement bathroom question. ;) Anyway, I'm putting in a shower/lav/toilet in a "un-roughed" basement. I know that I would like to use a studor vent but am unsure of the setup. Most of the stuff I have read have had them in order.. example; lav|shower|toilet, but my grouping is in a odd order. Could you please look at my diagram and tell me if either setup would work, or wich would work better. Thanks in advance. -Brian
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    May 27, 2005, 06:04 AM
    Quote Originally Posted by btk81
    Hello, After reading a few hundred posts and still not knowing what to do for sure i guess i'll have to ask speedball his millionth basement bathroom question. ;) Anyways, i'm puting in a shower/lav/toilet in a "un-roughed" basement. I know that i would like to use a studor vent but am unsure of the setup. Most of the stuff i have read have had them in order..example; lav|shower|toilet, but my grouping is in a odd order. Could you please look at my diagram and tell me if either setup would work, or wich would work better. Thanks in advance. -Brian

    Both layouts have the shower and lavatory draining into each other.
    You must maintain the flow twards the main. The top layout would be acceptable if the shower were to enter the lavatory drain with the flow.
    That means reversing the wye and connecting the shower with two 45's. However that would leave you with a return bend in the drainage. While in some cases it's necessary we try to avoid installing return bends in our drainage layouts. Also I would like to see some measurments between fixture traps and the vent. Regards Tom
    btk81's Avatar
    btk81 Posts: 3, Reputation: 1
    New Member
     
    #3

    May 27, 2005, 11:34 AM
    Thanks for the fast response Tom, Here's an updated picture of the meaurements. What would be the best way to route ths configuration? -Brian
    <img>https://www.askmehelpdesk.com/attachment.php?attachmentid=76&stc=1</img>
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    May 28, 2005, 01:40 PM
    Quote Originally Posted by btk81
    Hello, After reading a few hundred posts and still not knowing what to do for sure i guess i'll have to ask speedball his millionth basement bathroom question. ;) Anyways, i'm puting in a shower/lav/toilet in a "un-roughed" basement. I know that i would like to use a studor vent but am unsure of the setup. Most of the stuff i have read have had them in order..example; lav|shower|toilet, but my grouping is in a odd order. Could you please look at my diagram and tell me if either setup would work, or wich would work better. Thanks in advance. -Brian
    Brian,

    Go with the top layout only connect the shower reversing the wye and connecting into the lavatory drain with two 45's. That would leave you with a return bend in the drainage but in this case it's unavoidable. To lay it out any other way you would have to move some fixtures. Regards, Tom
    btk81's Avatar
    btk81 Posts: 3, Reputation: 1
    New Member
     
    #5

    May 28, 2005, 03:33 PM
    Sounds good Tom, thanks for the help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom in basement venting question [ 1 Answers ]

Hi, I know this has been asked before but I am still a little confused. We are going to instal a bathroom group in a basement. We are too far away from the main line and will need to vent the group but can't access any existing vents. My question is 1. Does the toilet need to be vented in...

Venting a bathroom group [ 2 Answers ]

Venting questions about a second floor bathroom: 1) Can I install a 2" vent behind a WC (the WC is at the end of the line and the vent rises upstream of the WV) and then connect a shower and tub (separate fixtures) downstream from the WC and consider them all vented? 2) Can I drain a pair of...

Basement Bathroom Venting [ 2 Answers ]

I had my rough in inspection yesterday, and everything looked good except my venting for my sinks. I am installing a bathroom lav and a wetbar sink, running into a 2" wet vent that already has a tub/shower on it. Since the distance to the furthest sink is just under 5' from the wet vent I thought...

Venting a basement bathroom [ 7 Answers ]

I have a rough in for a full bath in my basement. House was built in 2000 in Pa. Two story colonial. I can locate two vents from the 1st floor bath. One 2" vent right of the WC drain and one 1.5" off the shower on the first floor. There is a 2nd floor bath over the first. I can hear the 2nd...

Venting basement bathroom [ 5 Answers ]

Hi all, First time here. I am finishing my basement in Milwaukee. The washer dumps into a sink which has a 2" line that y's into a 4" drain that is stubbed up from the slab. This is not the main stack. The 4" ties to the main 4" about 12' away under the slab. The 4" stub rises from the...


View more questions Search