    SamAt's Avatar
    SamAt Posts: 8, Reputation: 1
    New Member
     
    #1

    May 23, 2009, 02:52 PM
    Recirc pump runs very hot
    Hi, I'm replacing a recirc pump while also installing a new water heater. It's a Taco 1/2" model and I'm concerned about how quickly it heats up and how hot it gets; concerned enough that I've not actually run it for more than 10 minutes for fear of damaging it.

    It gets almost too hot to touch, uncomfortable at least, even before the return water is hot (it takes about 5 minutes starting from cold until the return water is hot) am I correct in being alarmed?

    I know it is not pumping air because a) I have a clear pex section after it and could see bubbles and b) I have an air trap on the supply side.

    The pump is located on the return end of a loop that is almost 100 ft in length. It flows through a T, both lines have a check valve installed (yes, in the correct direction); one flows to the water heater supply line, the other to a tempering valve. Have I made an error here?

    Thanks much,

    Sam
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #2

    May 23, 2009, 03:11 PM
    Hi Sam,
    You have to bleed the lines after pump is installed. You have air lock in hot water system. Connect all pipes, activate pump. Go to all faucets in the house and run hot water for few minutes. Make sure the shut off valves are all in open position and that pump is not installed backwards. Remember, regular hot water recirculating pump is pulling water towards the heater, not pushing away from the heater. If installed properly, pump should be running very quietly and w/o vibration.
    SamAt's Avatar
    SamAt Posts: 8, Reputation: 1
    New Member
     
    #3

    May 23, 2009, 04:48 PM
    Hi Milo,

    Well I already did do all of those things so at least you've confirmed I'm thinking along the right lines. But based on your response I'm thinking there must somehow still be air in the system, but since the house has been active for a week and all hot water lines opened, where can it be hiding? The air trap before the recirc pump is not something I purchased; perhaps I installed wrong: it was empty before I installed, is that correct?

    I'll try the drain operation again anyway, thanks!
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #4

    May 23, 2009, 07:10 PM

    Bleed the pump itself. There should be Bleed Screw . Open it and let it run until it drips w/o any air coming out. Also, you probably have trapped air in the return line. So open faucets won't have any effect on it. You should have installed Auto-Air-Release valve, like Watts ( see the first photo ).
    Attached Images
      
    SamAt's Avatar
    SamAt Posts: 8, Reputation: 1
    New Member
     
    #5

    May 23, 2009, 08:19 PM
    The pictures help, thanks. I didn't realize the system supported it or I would have provided one. I'm configured as in the second diagram, except that the Taco cartridge recirculator does not have a bleed valve. Did I buy incorrect pump for the application?

    Appreciate your help very much Milo.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Well pump runs intermitten [ 7 Answers ]

I have a submersible pump 115 ft down. It has a Square D pump pressure control box. It is a 1/2 hp 3 wire pump with a control box near the well. The pressure tank has a bladder. My problem is that the pump stops at times. The pressure gage gets hung. The pressure control box contacts engage...

Well pump runs too often [ 6 Answers ]

When we use water in the house the well pump runs for about 1 second then is off for about 5 seconds and then repeats. Is this normal or shouldn't the pump run for a few seconds at a time? Would a water logged tank bladder cause this, and how do you fix the problem?

Water Hammering in hot H2O recirc system [ 10 Answers ]

I built this house on a slab 5 yrs ago. Well water to a storage tank to a booster pump to a pressure tank to the house. (2 story) Plumbing was initially laid in slab for Hot H2O recirc. On finish out with hot H2O tank upstairs plumbers installed recirc line to TACO pump T'd into cold side of...

Pump Runs and Runs Even When No Heat Is Needed [ 1 Answers ]

I have a 4 zone hydronic heating system. It is a 15 year old Hydrotherm HI-B series boiler with a new circulator pump. It has been noticed that when none of the zones call for heat and the boiler is back up to temperature the pump continues to run, a waste of power since al the zone valves are...

Why the Sump Pump runs now? [ 4 Answers ]

When I moved in here 2 years ago the sump pumps (have 2) very rarely came on - I did have backup issues (the sewer & sump pumps are on the same line) The reason was tree roots. Recently we decided to air compress the pipe lines to rid the roots. Now, all of a sudden my sump pump decides to run...


View more questions Search