    mooseye's Avatar
    mooseye Posts: 6, Reputation: 1
    New Member
     
    #1

    Oct 4, 2009, 03:21 PM
    Intertherm MAC 2460 troubleshooting
    I have the above electric furnace and I need some help troubleshooting it.
    I was able to make the unit work by jumpering a couple of the wires. I know this is not safe but so was freezing and I didn't leave it unattended. I have a meter and I have 240 volts to and out of breakers and to most of the wires on most of the components in the control panel. I need to know how and in what order to check the individual parts such as limits and sequencers.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 4, 2009, 03:56 PM
    First establish that it didn't blow out the transformer. Make sure you have 24VAC low voltage coming from LOAD/SECONDARY side of transformer.

    Also check for any blown fuses in circuit. Then jumper one limit switch at a time to see if any of those are open.

    That is a very old unit and I do not have a wiring diagram for it so you will just have to test the components as you choose.

    Need parts or other info go here and post your request under Nordyne since Intertherm is nor nordyne. These folks are pro's on mobile home units

    Index page
    mooseye's Avatar
    mooseye Posts: 6, Reputation: 1
    New Member
     
    #3

    Oct 4, 2009, 04:44 PM
    Thank you for your reply.
    I have signed up on the board you linked to but hae not yet received the activation email.
    I just checked every terminal on every componet and had either 121v or 30v.
    If I jump the connections on what I think are the sequencers, the element will heat up.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 5, 2009, 01:33 AM
    If you are jumping out the sequencers to get the heat on (elements on) then either the low 24 volt control voltage is missing that activates the sequencers or the 24 volt activation circuit in the sequencers themselves are defective. Remember the sequencers low voltage circuit also act as a simple time delay device to prevent initial high voltage circuit over draw and instant high voltage demand which will cause light bulb dimming and other such things. Also different sequencers will have different timing delay times so replacements should be of the same design and timing.
    mooseye's Avatar
    mooseye Posts: 6, Reputation: 1
    New Member
     
    #5

    Oct 11, 2009, 12:19 PM
    Quote Originally Posted by hvac1000 View Post
    If you are jumping out the sequencers to get the heat on (elements on) then either the low 24 volt control voltage is missing that activates the sequencers or the 24 volt activation circuit in the sequencers themselves are defective. Remember the sequencers low voltage circuit also act as a simple time delay device to prevent initial high voltage circuit over draw and instant high voltage demand which will cause light bulb dimming and other such things. Also different sequencers will have different timing delay times so replacements should be of the same design and timing.
    I have discovered that the control heater seems not to be working. The stage switches (sequencers) and a what I think is a limit switch are mounted on a metal plate assembly with the control heater inside. I assume that if the control heater is not working that the stage switches will not engage. Is this correct and can it be bypassed or will I need to replace the entire stage switch assembly?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Oct 11, 2009, 07:01 PM
    You cannot safetly bypass the controls.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Intertherm [ 1 Answers ]

Where are the reset button located on the inertherm. I know there are 4 please help.

Intertherm headache [ 1 Answers ]

My unit is an intertherm model E2EB-015HA the heat comes on but not the fan. Have replaced fan motcr ,replaced 1 breaker ,sequencer,and high limit thermostat. HELP!! Does anyone have a wiring diagram or know where online it can be acquired FREE?

Old Intertherm t-stat out,what to put in? [ 4 Answers ]

I have a mobile home with an Intertherm furnace, used for both heating ond cooling. I have one T-stat that controls which function is to be used,(heating/cooling). This one controls the cooling temp,and fan. I have a second T-stat that controls the heat temp. It is an old two wire mechanical and I...

Intertherm furnace [ 2 Answers ]

I have just in the last month had an Intertherm furnace installed, and since installation they have had to come in twice because they claim the starter button is not firing. They replaced it and now it is on the fritz again. It starts for about 8 seconds and cuts out. There is fuel in the tank....

Intertherm Furnace [ 1 Answers ]

My pilot light comes on and ignites heat exchanger but when the cover closes the flames shut down. The blower works but heat exchanger will not stay lit. I have replaced the gas valve and the thermo couple. Suggested that damper valve needed to be adjusted - where is the damper valve


View more questions Search