    mrjonm's Avatar
    mrjonm Posts: 4, Reputation: 2
    New Member
     
    #1

    Sep 18, 2005, 07:26 AM
    Loud Air Return Vent
    I have a small 850sqft condo. Lived her a couple of years. I have an old Borg Warner 65000 input BTU/HR unit. Model P3UGD080N6501A. Its an older unit. There is only one return in the condo which is located on the far side of the living room, connecting directly to the HVAC unit which is on the other side of the wall in the HVAC utility room. When the system kicks on, its so loud that I have to turn up the television, then turn it back down when the unit shuts off. The AC and Heat is working fine. Its not a defective noise, or a humming noise, its just a very loud wind noise as if it has a very powerful fan. Its always been this loud. The round turbo fan is located in the unit right on the other side of the wall of the return vent. I can see it right there when changing the filter. Is there any way to quiet or buffer this noise? Any suggestions would be highly appreciated.
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #2

    Sep 18, 2005, 08:58 AM
    Put up sound retarded insulation on the inside wall. That will help a bunch
    mrjonm's Avatar
    mrjonm Posts: 4, Reputation: 2
    New Member
     
    #3

    Sep 18, 2005, 09:41 AM
    Loud Air Return Vent
    The noise is coming straight from the return vent through the filter, since the fan is right on the other side of the filter.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Sep 18, 2005, 10:48 AM
    Have you turned it on with the vent and filter removed? It is possible the vent and filter is undersized for unit. My furnace has 2 filters almost as big as the hole into the furnace arranged in a VEE shape. Can you enlarge the vent, or add another one on a different side?

    You could also look at slowing the fan. Many fans have several speeds selected by connecting different windings to the relay that powers the motor. Too slow, and you could cause the coil to ice up.
    mrjonm's Avatar
    mrjonm Posts: 4, Reputation: 2
    New Member
     
    #5

    Sep 20, 2005, 04:07 PM
    Fan Noise
    The filter hole size is 20" by 14". I have tried it with the filter out, same results. No "V" shape. The unit is right up against the wall on the other side of the filter. Basically, you open the grid, remove the filter, and the fan is 8" in. I'm not sure I want to try to change the fan speed. Wouldn't that make the unit run longer to cool or to heat?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    Sep 20, 2005, 04:50 PM
    Many units are already set up to run slower in heating mode. In A/C mode, less, but cooler air would come out. Might or might not make much difference. Is the unit as noisy in heating mode?
    mrjonm's Avatar
    mrjonm Posts: 4, Reputation: 2
    New Member
     
    #7

    Sep 22, 2005, 04:17 PM
    Loud Air Return Vent
    Yes, it's just as loud with heating. It's the fan. Not a defective sound. Just wind sound. Wonder maybe since this is a very old unit, I could get a newer quieter fan?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #8

    Sep 22, 2005, 09:30 PM
    I think I have seen stuff on the angle of the fan blades. Some angles are more efficient, but noisier. Finding a better one that fits your furnace maybe tough. Not sure where to even suggest starting.
    ronny's Avatar
    ronny Posts: 3, Reputation: 1
    New Member
     
    #9

    Oct 10, 2005, 04:50 PM
    Had the same problem. Solved it today. My setup is different than yours so don't know if this will work for you. This was fairly easy and worked wonders.

    My CA unit sits about 20" off the floor and takes return air in from an empty area below it. My return and filter are at floor level and at right angles to the bottom of the unit.

    I installed a baffle at an angle between the return vent and the fan and covered the bottom side with some old carpet. This forces the air to make a bend after it flows over the carpet, which muffles the sound of the rushing air.

    This is hard to explain. Maybe the attached file will help, if I did it right.

    If you try something like this, just be sure you don't overly restrict the air flow. I can't help you with that.
    Attached Images
     
    jpadilla's Avatar
    jpadilla Posts: 9, Reputation: 1
    New Member
     
    #10

    Apr 30, 2006, 04:04 PM
    Quote Originally Posted by ronny
    Had the same problem. Solved it today. My setup is different than yours so don't know if this will work for you. This was fairly easy and worked wonders.

    My CA unit sits about 20" off the floor and takes return air in from an empty area below it. My return and filter are at floor level and at right angles to the bottom of the unit.

    I installed a baffle at an angle between the return vent and the fan and covered the bottom side with some old carpet. This forces the air to make a bend after it flows over the carpet, which muffles the sound of the rushing air.

    This is hard to explain. Maybe the attached file will help, if I did it right.

    If you try something like this, just be sure you don't overly restrict the air flow. I can't help you with that.
    But wouldn't this effectly reduce the size of the opening to the size of the opening is now the area under the baffle? My loud system is really bugging me but I'm concerned with this solution reducing air flow.
    ronny's Avatar
    ronny Posts: 3, Reputation: 1
    New Member
     
    #11

    Apr 30, 2006, 04:29 PM
    jpadilla, I'm not an A/C specialist, so take what I say with a grain of salt.

    I believe if you restrict the air flow too much, it will cause the sound of rushing air, perhaps a whistle, to become very noticeable.

    It is possible to determine the area (sq in) of opening necessary for your particular unit. You've just got to be sure you don't restrict beyond this point.
    Donald K's Avatar
    Donald K Posts: 8, Reputation: 1
    New Member
     
    #12

    May 13, 2006, 06:23 AM
    You can put the sheet metal baffle like the drawing and it will make the unit quieter. Would not recommend putting carpet on it though, carpet collects too much dust and other funky stuff after a very short while and if you have any allergies at all you will be in serious trouble. The sheet metal by itself will normally do the trick---just enough to make the air bend without going straight to the fan will normally do the trick. A rule of thumb for return air is whatever your a/c tonnage is (2 tons 12,000buth, 2 1/2 18,000btuh, (12,000 btuh per ton) take the tonnage ex--2 ton and multiply by 200---2x200=400 square inches of return air filter (20x20 filter--or any equivilent) and your airflow should be good.
    ronny's Avatar
    ronny Posts: 3, Reputation: 1
    New Member
     
    #13

    May 13, 2006, 10:48 AM
    Quote Originally Posted by Donald K
    You can put the sheet metal baffle like the drawing and it will make the unit quieter. Would not recommend putting carpet on it though, carpet collects too much dust and other funky stuff after a very short while and if you have any allergies at all you will be in serious trouble. The sheet metal by itself will normally do the trick---just enough to make the air bend without going straight to the fan will normally do the trick. A rule of thumb for return air is whatever your a/c tonnage is (2 tons 12,000buth, 2 1/2 18,000btuh, (12,000 btuh per ton) take the tonnage ex--2 ton and multiply by 200---2x200=400 square inches of return air filter (20x20 filter--or any equivilent) and your airflow should be good.
    Your point is well taken. I have found that the carpet serves to muffle the sound a little. Since my jerry-rigged unit is behind my filter and I clean my filter regularly as well as vacuum that little piece of carpet, I've had no trouble with it.

    Thanks for the formula.
    BILL60's Avatar
    BILL60 Posts: 6, Reputation: 1
    New Member
     
    #14

    Mar 1, 2007, 12:24 PM
    I live in a townhouse which I rent and it too has a loud noise of rushing air ocming out of the duct in the wall in the living room-the one closest to the furnace and blower which is just behind the wall. I have tried everything to cut donw on the noise to no avail-I vcut a piece of plexiglas to cover the ven and drilled holes in it to cut out the noise and it seems to work but it also cuts down on the maount of heat coming out. I see someone else wrote about baffling the incoming air under the furnace which is mounted about 20 inches off the ground so I am going to try this next. It drives me crazy that I have to keep turning up and down the TV when it is running so I can hear the telelvision but the mgnmnet says some of them are just like that. In other words, they aren't going to do anything. Oh yes-I didi oilt he motor since I figured that never gets doens but it made no difference. Any other suggestions?:) :) :)
    Donald K's Avatar
    Donald K Posts: 8, Reputation: 1
    New Member
     
    #15

    Mar 6, 2007, 03:46 PM
    It sounds like what you have is a bad ductwork installation.
    When you have a supply run coming off the main supply trunk (especially the first one) there is normally a baffle installed where the supply run comes off the main trunk. IF you have a baffle and can get to it adjust the baffle to decrease the airflow to this one run. IF you don't have a baffle or can't get to it take the plastic top off a coffee can, remove the supply grille (take the srews out) so you can cut the plastic the size of the ductwork feeding the grille----cut a smaller hole in the middle of the coffee can lid -- what you are doing is making your own baffle---try to get it back into the duct 4-6 inches if you can--put your grille back on that could solve the problem.
    Good Luck:confused:
    BILL60's Avatar
    BILL60 Posts: 6, Reputation: 1
    New Member
     
    #16

    Mar 7, 2007, 10:11 AM
    Thanks for the advice but I already used a [iece of plexiglass which I cut to the size of the vent and I drilled holes evenly spaced in it to allow for the air to come out but I didi try putting a piece of rug underneath the intake area before the filter and that seems to help a lot. The main vent from the hot air flow has two roubd vents before it comes out the register closest to the vent in my living room-the loudest one, I had put one of those pieces of filter foam to filter the air. Any other ideas would be helpful. Thanks
    OrlandoCreative's Avatar
    OrlandoCreative Posts: 1, Reputation: 1
    New Member
     
    #17

    Aug 13, 2009, 12:18 PM
    Quote Originally Posted by ronny View Post
    Your point is well taken. I have found that the carpet serves to muffle the sound a little. Since my jerry-rigged unit is behind my filter and I clean my filter regularly as well as vacuum that little piece of carpet, I've had no trouble with it.

    Thanks for the formula.
    They make sound dampening products such as this that help with HVAC or vents. I have the same problem with my AC unit (older home with central air added later). I think I will use a baffle and the sound material.

    Echo Absorber Natural - echo and noise eliminator
    Testecha's Avatar
    Testecha Posts: 2, Reputation: 1
    New Member
     
    #18

    Sep 10, 2009, 08:24 AM
    I have the same return air vent noise problem. Is it true or has anyone heard that significantly lengthening the return air duct greatly reduces the noise at the vent filter?
    Thanks for any help provided.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #19

    Sep 10, 2009, 05:32 PM
    Duct properly sized has a way of making the system much more quiet especially on the return side. Many units have little or no actual return ducts and under those conditions the systems are very loud from the blower system itself. There is NO magic cure that works 100%.
    Testecha's Avatar
    Testecha Posts: 2, Reputation: 1
    New Member
     
    #20

    Sep 11, 2009, 06:46 AM
    My ducting is the flexible insulated duct. It is about 6 feet from the unit to the return vent grille. Would it get quieter if I added 10 or 15 feet of duct to the existing duct?
    Thanks
    Test tech a

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New A/C loud wind noise velocity on air return [ 1 Answers ]

We are building a vacation home on Eleuthera in the Bahamas (very pretty and very hot). The house is 1000 square feet inside with an exposed beam cathedral ceiling in the main room and 10 foot ceilings in the two bedrooms and a small hallway that connects all three rooms. The Bahamian builder put...

Basement return air vent [ 2 Answers ]

Carrier, modal 58MAC120-20, direct air forced air furnace, seven years old in a 2,700 square foot home seven years old. The basement is 1,200 square feet, open and half finished, has two supply air regesters and no return air vent. What size "opening" is recommended for this area?