  • Dec 17, 2006, 01:34 PM
    gks
    What are the Bryant 373LAV/376CAV Error Codes?
    I have a Bryant 373LAV/376CAV Gas Furnace. I started having a problem with it and can't find the FLASHING LED ERROR CODES anywhere. After reading some of the answer in these forums I'm assuming the LED flashes x times short, then x times long for a 2 digit number. I'm getting a 3 short 3 long flash which I assume is code 33.

    Here is the scenario.

    The system goes through the normal startup cycle like this (just so you-all know that I know what is normal):

    Power on the unit
    LED comes on solid red
    Turn on and up thermostat (call for heat)
    Small fan turns on
    10+ seconds go by
    Glow starter lights up
    15+ seconds go by
    Gas valve opens
    Burners come on
    45-60 seconds of warm up time
    Blower motor starts

    After a while, the gas shuts off and the error code 33 starts flashing (thermo is still calling for heat).

    If I turn off power to the unit (to reset it) then power it back up, the blower motor come on right away and the error code changes to 12. After a short while the LED goes solid red again and the heat cycle starts again like normal and it fires up again.

    SO... what is code 33? Loss of gas? Overheating due to maybe clogged filters? All I can do is guess until I have these codes. WHERE CAN I GET THE CODE? WHERE CAN I GET A SERVICE MANUAL? Stupid Bryant web site does not provide any helpful info at all!! Too bad for the do it yourself person!

    THANKS FOR ANY HELP!!
  • Dec 17, 2006, 02:40 PM
    NorthernHeat
    Codes are on the front of the blower door. Sounds like the flame sensor is dirty and it is sensing a weak flame, just my best guess from here.
  • Dec 17, 2006, 06:07 PM
    gks
    Quote:

    Originally Posted by NorthernHeat
    codes are on the front of the blower door. Sounds like the flame sensor is dirty and it is sensing a weak flame, just my best guess from here.

    33 - Limit or flame roll-out switch is open

    Doah! I looked and there they were, plane as day, the codes, right on that stupid sticker on the cover!! Sorry, I guess I was so focused on one thing I missed the obvious. I even DID read the sticker on the cover for the propane conversion, but didn't see the code sticker!!

    Anyway, I didn't include all the "possible reasons" for this, too much to type, but one of them did say something about restricted air flow. So that's what I'm testing now. Cleaned the filters and opened all the registers to max, just to see if the problem goes away...
  • Dec 18, 2006, 01:50 PM
    gks
    That seams to have done the trick. Not a day too soon either. The temp this morning was 27! So I guess I had restricted airflow. I will keep watch on it for a few more days and report back if anything changes.