    Furnace blows cold air briefly several times a day
    Goodman GMP-075-3 gas furnace circa 1994 (induced draft, hot surface ignition, ca. 80% efficient, horizontally mounted in unheated attic, no A/C). Honeywell Magistat thermostat.

    The furnace worked fine for about 8 years, and still heats well and maintains the proper temperature. Starts with an exhaust blower for about 15 seconds to clear the flue of gases, then the burner ignites for about 15-30 seconds, then the air circulation blower starts. When the thermostat is satisfied, the burner turns off and the blower runs for another couple of minutes to extract the last of the heat from the system. The temperature and velocity of the air coming from the registers is normal.

    The problem is that several times a day the furnace blower will come on and blow air for a couple of minutes while the thermostat is not calling for heat, and then turn off. Sometimes it even happens shortly after the thermostat has gone into overnight mode and the temperature setpoint is 10 degrees or more below the room temperature. In the past it did it with the thermostat off.

    This started about 2 years ago at the end of the heating season when the temperature got warmer. But when I turned on the furnace last year in the fall the problem didn't show up... so we used the furnace all of last winter... until the problem came back last spring at the end of the heating season. This fall the problem showed up as soon as we started using the furnace and it has continued since then.

    I install a new thermostat when the problem first showed up (the current Magistat) and that did not correct the situation. So I don't think that it's the thermostat.

    Any suggestions on things I can check? The symptoms sound similar to the posting #91, but that one doesn't seem to have been resolved. If it's the circuit board, can you recommend a good source on the internet?

    Thanks in advance for your help.
    bharr07's Avatar
    bharr07 Posts: 22, Reputation: 1
    New Member
     
    #2

    Nov 25, 2006, 09:43 PM
    Try replacing the delayed fan timer located in the fau , this is probably where your problem lies
    bkspero's Avatar
    bkspero Posts: 33, Reputation: 2
    Junior Member
     
    #3

    Nov 25, 2006, 10:11 PM
    Quote Originally Posted by bharr07
    try replacing the delayed fan timer located in the fau , this is probably where your problem lies
    Sorry for my inexperience, but I'll need more details. I can't find a "delayed fan timer" in the repair parts lists/diagrams or in the installation and operating instructions. And I'm not familiar with the term fau. I've been assuming that the fan timing happened on the circuit board (the circuit board is actually named the "Fan Control/Ignition Module). There is nothing that I can construe as a timer on the blower motor or fan housing drawings.

    Where should I look for this device?
    bharr07's Avatar
    bharr07 Posts: 22, Reputation: 1
    New Member
     
    #4

    Nov 25, 2006, 10:35 PM
    I myself am not familiar with some model numbers on goodman fau"s (forced air unit) but I know now what type you have and your problem is this fan control mudule , not diffucult to replace , its located in the blower unit compartment , it sounds like you can read your wiring schematic in your owners manual , get yourself the new module and replace wire for wire, remember shut all power off to the unit before toching anything
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #5

    Nov 26, 2006, 06:50 AM
    Replace the PC board it can be the only cause I can think of. Also when was the last time you had a safety inspection on that furnace, I'll bet you all the rivets are broken, your health is worth more than a new furnace.
    bkspero's Avatar
    bkspero Posts: 33, Reputation: 2
    Junior Member
     
    #6

    Nov 26, 2006, 07:04 AM
    Quote Originally Posted by NorthernHeat
    Replace the PC board it can be the only cause I can think of. Also when was the last time you had a safety inspection on that furnace, I'll bet you all the rivets are broken, your health is worth more than a new furnace.
    Thanks all for your input. I will replace the circuit board and see if that corrects the problem.

    As for the safety inspection, I do my own every year when I start up the furnace. Two years ago that included removing the plenum and checking the exchanger from the top as well. There didn't seem to be anything broken.

    I checked the records and the furnace is actually 12 yrs old, so it was 10 yrs at the time). I will take a look at it again when I'm replacing the circuit board.

    By the way, I have a CO detector with a digital readout that gets nearly direct exposure to the air from one of the registers, and its reading is zero and stays zero when the furnace is heating. I can't vouch for the detectors calibration, but the readout does respond to an external source of CO when I've tested it.

    Will let you know what happens with the circuit board.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #7

    Nov 26, 2006, 07:24 AM
    Quote Originally Posted by bkspero
    Thanks all for your input. I will replace the circuit board and see if that corrects the problem.

    As for the safety inspection, I do my own every year when I start up the furnace. Two years ago that included removing the plenum and checking the exchanger from the top as well. There didn't seem to be anything broken.

    I checked the records and the furnace is actually 12 yrs old, so it was 10 yrs at the time). I will take a look at it again when I'm replacing the circuit board.

    By the way, I have a CO detector with a digital readout that gets nearly direct exposure to the air from one of the registers, and its reading is zero and stays zero when the furnace is heating. I can't vouch for the detectors calibration, but the readout does respond to an external source of CO when I've tested it.

    Will let you know what happens with the circuit board.
    The heat exchanger is held together by what they call rivets they are the hole you see in the walls of the heat exchanger cells, when the break you will just fing dime sized rings laying around in there.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gas Furnace Blows Cold Air [ 18 Answers ]

This actually just started a day ago and I am trying to figure out as much as I can before calling a service person (if necessary). My apologies in advance if I am leaving out important details but I've never dealt with a faulty heater or A/C before. My central heater in the attic was running...

Forced air furnace blows cold at first... [ 7 Answers ]

Hi all, I found this forum full of helpful answers, so I'm hoping will be able to get some ideas on what could be wrong with my heating system. Iam using forced air furnace, that was working fine last year blowing hot air. However, this fall soon after turning it on, cycle starts but blowing...

Cold Air Duct Return Blows Instead of Sucks [ 16 Answers ]

HI, I need your help. I have purchased a home that has a new Hi-Effency forced air furnace. The house has a 2 1/2 ft crawl space - no basement. The heating and return ducts are below under the floor boards of the house in the crawl space. The crawl space is insulated as are the ducts. My...

Gas furnace blows out cold air at night [ 3 Answers ]

Hi there. I have a problem that I haven't quite seen here and I have no idea how to search for it. Here's the deal: I have a gas furnace. I'm trying to save energy, so I got a new thermostat at the beginning of the fall. I set it to 68 when we're awake and in the house, and 60 after 10pm and...

Heater blows warm air but also cold [ 1 Answers ]

Our heater blows warm air out as it is supposed to, but also blows cold air out of the cold air return vents. Any idea on how to fix this short of replacing the system?


View more questions Search