    Furnace not igniting - Rheem Criterion
    I have a Rheem Criterion furnace, about 10-11 yrs old. It turns on, the blower starts, no ignition. It cycles a few times but no ignition. I replaced the ignition, but nothing. There are no error messages on the board. Anything I can check before calling a technician?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Feb 5, 2010, 04:25 PM

    Does your system have a hot surface igniter, or a spark igniter. How many pressure switches are in the unit? Check to make sure that the pressure switch tube port on the draft inducer is not plugged.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #3

    Feb 5, 2010, 04:27 PM

    It is a hot surface igniter - it glows. Sorry, you lost me with the rest. I'm not sure where to look.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Feb 5, 2010, 04:33 PM

    Okay, first, is the igniter glowing at all? The reason I ask, is because I need to know exactly what you mean by "no ignition". Is igniter working, but the flames won't ignite, or does the igniter simply not glow at all.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #5

    Feb 5, 2010, 04:40 PM

    The tube on the pressure switch looks good. I only see 1 pressure switch.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #6

    Feb 5, 2010, 04:41 PM
    The igniter doesn't glow at all. I replaced it today. I was careful not to touch it as well.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #7

    Feb 5, 2010, 04:44 PM

    Sorry man, wish I could help, but duty calls, got to go on a furnace call, so I hope to be back tonight, or ill check in with you tomorrow.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #8

    Feb 5, 2010, 04:45 PM

    Thanks for the help.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #9

    Feb 6, 2010, 02:33 PM

    Okay, you said the blower starts. By blower, do you mean the big blower that circulates air in the home, or the small blower that exhaust burnt gases.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #10

    Feb 6, 2010, 03:26 PM

    The small blower.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #11

    Feb 6, 2010, 04:17 PM

    Turn furnace off, then, disconnect the tube that hooks between the pressure switch and the draft inducer(small blower) from the draft inducer(leave it hooked to pressure switch. Then turn the furnace back on. As soon as the small blower starts to run, lightly suck on the tube going to the pressure switch, keep sucking for about thirty seconds, or even longer. See if the igniter glows now, and if flame lites. Let me know. If not we will take the next step.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #12

    Feb 6, 2010, 04:42 PM

    Good call. I did as you described, and the igniter started to glow. The furnace seemed to run normal after that - that is to say, it ignited the gas and the big blower turned on.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #13

    Feb 6, 2010, 04:55 PM

    Good, now, the port on the draft inducer where you unhooked the hose, check to make sure it is not plugged up in any way. You can use a paper clip and stick it in there to clean it out. Then hook the hose back up and let me know if the furnace works properly. Ill be here for a little while so let me know asap.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #14

    Feb 6, 2010, 05:07 PM

    The port has a little gray piece over it - because of that piece I couldn't stick the paper clip into it. I checked the hose to make sure there were no clogs.
    When I turned the furnace back on and set the thermostat to call for heat, it appears to be working normal.
    Two questions - what was the problem? And If it stops working in the next few days, what would you suggest I check or replace?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #15

    Feb 6, 2010, 05:12 PM

    That's a hard call. Without being there to test things for myself, I don't like to suggest replacing parts, however in your case, I would start by replacing the pressure switch, they are fairly cheap and easy to replace. Glad to hear the furnace is working. Come on back if any further issues arrise. Take care. Lee.

    PS. Make sure you are sticking the paper clip into the draft inducer(small blower) not the pressure switch.
    rduncanson's Avatar
    rduncanson Posts: 9, Reputation: 1
    New Member
     
    #16

    Feb 6, 2010, 05:15 PM

    I was definitely trying to stick it into the wrong part. Good tip. Good thing they idiot proofed it for us idiots.

    Thanks again.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #17

    Feb 6, 2010, 05:20 PM

    Ha ha. Yep, your lucky your pressure switch has the restricting device, or you may have ruined the switch. But as it is, no harm done.. Like I said, I'm just glad your back in heat, and let us know if you have any more questions.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Rheem criterion II heating furnace [ 1 Answers ]

Furnace makes a loud vibration noise when turned on as if it is out of balance. How do I correct this problem.

Furnace rheem criterion [ 1 Answers ]

Furnace blower fan and the pre blower fan come on at same time. And the ignitor won't light. Have to turn off power switch to stop both fans. I changed upper limit swith but still won't work. When it was working it was going great, returned and blower was running only but no heat. Thermostat...

Rheem criterion II gas furnace [ 3 Answers ]

Have a rheem furnace and when it turns on it blows real hard something I read said it has a three or four speed motor just wondering if some one could help me change the wires to lower the speed of the motor

Rheem criterion furnace [ 3 Answers ]

My air went out yesterday and I don't what to do... the motor outside is not working but the inhouse fan is work air is coming out of the vent but it is not cool. This happened in the winter and we had the heat ignaitor replace... help?? it 98 degree today


View more questions Search