    I have a carrier weathermaker downdraft heat&ac unit that fails to open the gas valve soon enough after the ignitor is glowing before it cycles through another attempt or "locks out".
    With the inducer motor running and ignitor glowing good either nothing else happens or a hissing noise like a servo motor comes from behind the top panel where the circuit board is before the click of the gas valve opening, but too late because the ignitor has "timed out" for the next attempt (or lock out).
    If I restart the unit enough times it will finally open the gas valve soon enough to light and maybe continue automatic operation through the night heat demands only to fail the next evening after no demand during the day.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 8, 2009, 12:09 AM
    Attach meter to gas valve 24 volt terminals. Watch to see if 24 volts present when gas valve does not open. If 24 volts present and gas valve not open you have a bad gas valve or actually a slow responding gas valve and it should be replaced. Now if the 24 volts is not present or delayed then your problems are elsewhere.
    thinkalot's Avatar
    thinkalot Posts: 9, Reputation: 1
    New Member
     
    #3

    Nov 8, 2009, 12:28 AM
    The gas valve clicks open as soon as it receives the 24.7 volts. It just receives the power signal too late in the sequence to catch the hot surface ignitor still glowing (which has been glowing for approx 42 secs) to light the burners.
    There seems to be a "pregnant" delay to open the gas valve?
    I don't know what the hissing noise like a servo motor coming from behind the top panel where the circuit board is before the click of the gas valve opening is?
    If the gas valve would receive the power signal as soon as that hissing event, it would be soon enough in the cycle to ignite the burners, I think.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 8, 2009, 06:14 AM
    It seems the circuit board is causing the problem since you say the gas valve opens as soon as it gets the voltage. I just love that term pregnant delay. That is a new one for me. Post exact model number and I will see if I have any other info since there are a few other controls in the command line for proper operation.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Nov 8, 2009, 01:10 PM
    I am seeing a rash of this lately, both here and in the field. Try this: jumper the "R" & "W" terminals on the furnace circuit board & observe operation. A faulty thermostat may not be maintaining adequate control voltage under load, and introducing the gas control to the load could be exceeding the thermostat's ability.
    thinkalot's Avatar
    thinkalot Posts: 9, Reputation: 1
    New Member
     
    #6

    Nov 11, 2009, 10:46 PM
    KC13, I inspected the thermostat after I took the reading when the gas valve did open and was satisfied that it was just too late.

    hvac1000, as far as I could gather the gas valve never failed to open once it received the power signal.

    I got too single minded with the timing so I started to try to troubleshoot the circuit board.
    I discovered I mischaracterized the "hissing" noise which was actually the gas valve relay "buzzing" before it positively closed turning the gas valve on so I swapped it out with the unused humidifier relay. The results were the same so I theorized there was a lack of adequate control voltage for the relay to "make". While inspecting the board I didn't like the presence of heat discoloration and corrosion on a few resistors (and was getting exasperated) so I ordered an ICM281 board from Patriot Supply.

    Replaced the board and got ignition on first attempt.
    Maybe next time I'll contemplate whether it was low control voltage or "retarded" cpu timing due to deteriorated components, or...

    After the first successful ignition I had to swap the "standoff?" pegs from the old board that I forgot. When the next heat demand came on to prove normal operation the blower came on and stayed on and the board gave me a 33 flame rollout failure. WHAT NOW? I checked the limit swiches, cursed a lot, and thought about how nice a nursing home might be. Okay, so I forgot to plug the board back in the last time, I still know where I live, I think.

    Thanks for the help.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Nov 12, 2009, 03:46 AM
    What is the complete model & serial #'s of this unit? I hate to say it: I've seen the aftermarket board & don't care for it.
    thinkalot's Avatar
    thinkalot Posts: 9, Reputation: 1
    New Member
     
    #8

    Nov 13, 2009, 10:54 AM
    KC13,
    I wasn't straight forward with my last answer. The ICM281 board from Patriot Supply is working perfect (so far). I just told on myself for forgetting to plug the limit switches terminal back into the board when I first allowed the unit to perform the final normal operation proof (It didn't know any better, that was on me).
    The repair was successful. No problems now.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane xe80 gas furnace not blowing any hot air [ 2 Answers ]

I have a Trane XE80 Gas Furnace. It is not blowing any hot air at all. Can anyone help. Thank you

Carrier gas furnace code 31 [ 3 Answers ]

Hi. I have a Carrier gas (propane) furnace 58MCA100-11116 series 111. It shows a code 31. The evacuation blower runs for a short time then kicks off. The burners do not ignite. To date I have: replaced the pressure switch, checked in and out lines to the pressure switch for obstruction,...

Blowtorch sound when gas valve opens.Intertherm propane furnace. [ 1 Answers ]

I have an Intertherm model MGHA-056AAFC-05 propane furnace with pilot light in a park model trailer.Its 12 years old and used sparingly.Almost since day one it will intermittantly fire up with a blow torch sound and when the blower motor cuts in... the flame will go out and it will shut down. I...

Carrier Natural Gas Furnace main gas valve will not open every call for heat [ 1 Answers ]

We have a Carrier Weather Maker 8000 Natural Gas Furnace not functioning properly. We have replaced pressure switch, hot surface ignitor, flame sensor and control board. It will cycle 3 to 4 times and then not come back on. Is it possibly a bad coil on gas valve?:rolleyes:

Carrier furnace gas valve won't open [ 8 Answers ]

Hello, My carrier furnace is on the fritz. I am receiving a 34 code which states"ignition proving failure" The blower fan starts and the hot surface ignitor lights but no gas flows. I replaced the ignitor with a new one-no help. The flame sensor is clean.When I check voltage at the gas valve...


View more questions Search