    Water Heat Vent Fan runs constantly
    I have a 75 Gallon Natural Gas State Select Water Heater. Model # PR675NRVTZ. It has a fan on top that vents the gas to the outside. Normally, this fan only runs when the water is being heated. Now, the fan runs constantly eben when the water is not being heated. I do not have the wiring diagram, however I found a "switch" that if I unplug it will turn off the fan. The switch has 2 terminals. It has 4 screws that bolt it to what I believ is the gas valve. I ohm'd the switch out and it reads 0.00 (closed). Before I go and replace it, does anyone know if that switch is supposed to read 0.00 only when triggered and open line when not? If so, what triggers that switch and how can I test that other part? Thanks, Vin
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Nov 7, 2006, 10:32 AM
    You may be ohming the wrong switch. There could be a limit switch further into the combustion area that is giving a false over temperature reading. Or a relay could be stuck. Do some more checking before replacing a part that may be doing its job.
    VIN442's Avatar
    VIN442 Posts: 4, Reputation: 1
    New Member
     
    #3

    Nov 7, 2006, 10:58 AM
    Quote Originally Posted by labman
    You may be ohming the wrong switch. There could be a limit switch further into the combustion area that is giving a false over temperature reading. Or a relay could be stuck. Do some more checking before replacing a part that may be doing its job.
    Labman, There is one other sensor at the top of the unit in the "Gas Hat" where the fan is. It also ohm'd out at 0.00. I unplugged that sensor and the fan keeps running. Any idea what that reading is supposed to be? Thanks again, Vin
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Nov 7, 2006, 11:36 AM
    If it is a switch, it should either be zero or open. Thermisters are becoming more common. I asked the moderator to move this to H&C where our top man will see it.
    VIN442's Avatar
    VIN442 Posts: 4, Reputation: 1
    New Member
     
    #5

    Nov 7, 2006, 04:59 PM
    Quote Originally Posted by labman
    If it is a switch, it should either be zero or open. Thermisters are becoming more common. I asked the moderator to move this to H&C where our top man will see it.
    Labman, I read this posting (https://www.askmehelpdesk.com/plumbi...ter-33192.html) and lightly tapped the switch that was shown and the fan went off as it should. I then ran the hot water, waited and the flame and the fan came on and then went off as it should. I would surmise now that the solenoid is defective. Thank you for your help, Vin
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #6

    Nov 7, 2006, 05:13 PM
    Yes, it sounds like the blower relay stuck closed. This is caused when the relay closes the is an electrical arc which pits the contacts and can cause them to weld themselves closed. When you tapped it it become unwelded. Now that the contacts have become so pitted and worn this will happen more frequently. It is better to just go ahead andget it replaced. It is used so a low voltage demand can be sent to the aquastat and gas valve, and to close the circuit for the blower which is 120 volts. If this helps you narrow down where it might be located for sure.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump AHU fan runs continuously [ 2 Answers ]

I have a 12 year old Trane Xe1000 heat pump. Recently I noticed that the fan keeps running continuously even when the outside unit turns off. It's as if the tstat fan switch is set to On (it's not) instead of Auto. I tried a few things: 1) In the tstat (weathertron) I disconnected the fan...

No heat, blower runs constantly, carrier gas furnace [ 7 Answers ]

This am we I got up the blower on my carrier series 100 gas furnace (approx 10 years old)was running and blowing out cold air. Even with the thermostat turned to off the blower runs constantly. The only way to stop the blower from running is to turn the switch on the side of the furnace to off or...

Fan constantly blowing [ 3 Answers ]

A couple of years ago, I replaced our old mercury style thermostat with a digital one. It worked fine for a while. Maybe a year later, we noticed that the heat would kick on and off fine, however, the fan blows constantly (usually blowing unheated air). The only way to turn off the blowing is...

Inside fan runs, outside fan runs, but air is not cold [ 8 Answers ]

The inside fan runs and runs, the outside fan on the compressor runs and runs, but only hot air comes out. I sprayed the outside compressor coils with the garden hose to clean them and checked the inside filter. Is there something else I could check? Thanks


View more questions Search