    Byrant Plus 90 furnace will not relight
    I have a 1987 Byrant Plus 90 furnace. The other day the wheel on the inducer motor lost a couple of blades. I replaced it installed a new wheel and the motor. Plugged everyhting in but the pilot light would not stay lit. I removed the cover cleaned the pilot light area and the gas orfices. The furnace will light and cycle when the covers are off. But once I put the covers on it will not relight. I removed a small amount of debris form the exhaust pipe, which had water in it. Does anyone have any ideas why my furnace will not relight?
    Thanks
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 6, 2008, 09:39 AM

    This is a model 398... A or B? Sounds like an obstruction in the combustion air intake. Check the strainer in the top of the burner box by removing the pipe on top, also check the vent termination outside. Use a shop vac if possible to suck out the intake and exhaust pipes. It would also be a good idea to flush the condensate trap (located on the front of the blower) to assure the secondary heat exchanger is not flooding. Let me know...
    304jasonm's Avatar
    304jasonm Posts: 5, Reputation: 1
    New Member
     
    #3

    Dec 6, 2008, 10:16 AM
    Thanks for the quick response. I did clean the intake screen on top. I am now in the process of trying to remove the intake pipe to check and clean. I'm just trying to figure out why this relight problem would start exactly the same time the inducer motor wheel broke. Hopefully just a coincident and the vibrations of the out of balance motor did not cause some other problem.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Dec 6, 2008, 02:25 PM

    Another thought... did you find the vanes that ejected from the old inducer wheel? If they collected in the inducer housing outlet or exhaust pipe, they could be spoiling the flow through the exhaust vent, preventing the pressure switch from engaging. Did you notice a sulfuric odor when changing the inducer? This might indicate a restricted secondary heat exchanger. More info available at furnaceclaims.com.
    304jasonm's Avatar
    304jasonm Posts: 5, Reputation: 1
    New Member
     
    #5

    Dec 7, 2008, 02:44 PM
    I found 1 of the 3 blades. I looked everywhere and could not locate the other 2 blades.
    The furnace will relight and operate if I take the little inspection glass cover approx. 2" across out of the door for the pilot light/burner housing. Also I have to leave the top cover off the furnace. It's like the pilot light is not getting enough oxygen.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #6

    Dec 7, 2008, 03:40 PM

    I would be more suspicious that the pressure switch is not engaging when the covers are in place. A voltmeter connected to the p/s would be useful to determine if this is the case. Try this: put the covers back on and remove the air intake pipe from the top. Start up unit, wait until unit preheats and blower starts, then reconnect intake pipe. If burners drop out, the pressure switch is re-opening.
    304jasonm's Avatar
    304jasonm Posts: 5, Reputation: 1
    New Member
     
    #7

    Dec 10, 2008, 09:22 AM
    When I take the intake line off, the furnace seems to operate properly, (with all covers on)
    I have removed the intake line to inspect for any obstructions, there are none.
    Any ideas? Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Cannot relight gas water heater pilot light [ 2 Answers ]

After I light it, my gas water heater pilot light always goes out when I release the pilot light knob. This occurs regardless of how long I have been depressing the knob (usually several minutes) to keep the pilot light going after I have ignited it.

Goodman gas furnace.relight after turning off gas at meter? [ 1 Answers ]

Hello, First time posting. Maintenance tech at local college. I'm working at home today though. I am relocating a gas line in the living room and need to turn the gas off at the meter. We have a Goodman gas furnance(duel fuel system)with electronic ignitnor. When I turn the gas to the house...

Byrant heater will not light [ 1 Answers ]

I have a bryant heater that will not light Model #394GAD036100. I think it s the ignitor as I had to relight it before but I am not sure

Furnace not heating the house. Damper on the furnace not opening. Motor then shuts. [ 4 Answers ]

My forced-air furnace is not working correctly. The gas works heating the air in the furnace, but When the motor starts the damper doesn't open and the Motor shut down. I need suggestions?:mad:


View more questions Search