    Honeywell RTH230B A/C Auto Fan not working
    Hello,
    We installed the Honeywell RTH230B thermostat this January and it worked fine with our gas furnace. The problem is when we switched the control to cool yesterday the compressor turns on but the fan won't work in auto mode. It does work if I turn it to on mode only. Any ideas why the auto mode won't work? Thanks!
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Apr 14, 2006, 08:32 PM
    There is an internal jumber built into the thermost that sends power to the blower relay at the same time it sends power to the AC contactor. So if your furnace or air handler is new enough then you probably have a printed circuit board, and if you do some boards have hard wired relays and some have plug in relays. You need to find the relays on the circuit board and getnly tap each one to see if any thing happens. It is possible that there is a cold solder joint and by taping it you might cause it to make contact and the blower might come on. If you have a door switch you will have to make sure the switch is depresed to make this test, you can depress it by putting some duct tape over it temporally. Also there should be test points where you can short across them and each operation should come on indivigualy except for the gas on mode.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Honeywell RTH230B [ 3 Answers ]

I currently have a very old thermostat, White-Rodgers 135-415, which I'd like to convert to a Honeywell RTH230B. Currently there are only 3 wires that are connected to the thermostat (which is only for my apartment's heat. White wire is connected to what looks to be labeled "Common" Black...

Honeywell rth230b [ 4 Answers ]

This winter I installed honeywell rth230b. Heater works great, but I have no a/c. I have 6 wires from wall. Rh--red Rc--blue W--white Y--yellow G--green Brown not being used Help it is 90 deg. I need my a/c Thank you all

Honeywell RTH230B A/C Fan Not Working [ 3 Answers ]

I've read numerous threads on this model but could not find a solution. I just replaced my old thermostat with this model. The wiring on the old thermostat went as follows: Red - Rc jumped to Rh White - W Green - G Yellow - Y When I removed the old thermostat I noticed there was a blue...

Honeywell RTH230B [ 6 Answers ]

I am installing a Honeywell RTH230B thermostat but am not sure of the wiring. I have 6 wires colored as follows, red, green, white, yellow, and 2 blue wires. Please advise?

Honeywell rth230b- heat is working but not the air conditioning [ 1 Answers ]

A friend of mine replaced my thermastat with the Honeywell rth230b. The heating is working but the air conditioning is not. I have checked to make sure the breaker wasn't tripped. What else could be the problem?:confused: Thank you:


View more questions Search