    Heat pump reaches setpoint but won't turn off
    Hi...

    I have a Janitrol heat pump (I don't know the model number) controlled by a Robertshaw thermostat (model #9520).

    I am having a problem with the heat pump warming the house to the normal setpoint for comfort (say, 70 or 71) during the day but the heat pump continuing to run. By continuing to run, I mean the whole system, inside and outside units (fan, compressor unit).

    Today, we are having temps in the mid- to upper-40s. I had I lowered the setpoint to 66 and the unit would turn itself off. However, if I raise the setpoint, the problem with it continuing to run recurs.

    On especially cold nights (in the 30s or even into the high 20s), the heat pump will run for hours without cutting off and it doesn't appear that the auxiliary heat ever comes on.

    I called an HVAC service to come out Monday (Christmas Eve) and the tech looked things over. He said the refrigerant level, compressor, defroster, heat strips, etc. all seemed fine. He pressed the reset switch on the thermostat and said that might clear it up. If not, he said I may need a new thermostat.

    He explained how auxiliary heat worked and said that if it's cold enough outside for the heat pump to not warm house sufficiently to shut the system off, the auxiliary heat should kick in to help to reach the setpoint. (He also said that if the heat pump warmed the house to setpoint, but the unit continued to run for a lengthy time, the auxiliary heat should come on long enough to help the unit shut off.)

    Today's example, as I type: I had the setpoint at 66 since this morning. While reading over this site, I reset the thermostat to 69. The unit has raised the temp to 69, but now the heat pump is continuing to run and there is no sign of the auxiliary heat coming on, although the setpoint of 69 was reached 15 minutes or so ago.

    It sounds reasonable to me that this may be a thermostat issue, but I wanted to see if I could find any other information/assistance that might help confirm that diagnosis before I purchase a new thermostat.

    The tech also advised that if I go with a new thermostat, to stay away from Hunter and preferably go with a Honeywell. Your thoughts on that would be appreciated as well.

    Thanks!

    --Paul

    UPDATE: about 25-30 minutes after reaching the setpoint of 70 this afternoon, the unit just shut off.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 26, 2007, 12:44 PM
    Honeywell all the way.
    Someone needs to check your aux/strait electric heater circuit unless you already did that. Turn the stat all the way up and see if the electric heat turns on. If it does it could be the stat. If it does not it could be the stat or a component in the electric heat circuit.
    Auburner's Avatar
    Auburner Posts: 9, Reputation: 1
    New Member
     
    #3

    Dec 26, 2007, 12:47 PM
    Quote Originally Posted by hvac1000
    Honeywell all the way.
    Someone needs to check your aux/strait electric heater circuit unless you already did that. Turn the stat all the way up and see if the electric heat turns on. If it does it could be the stat. If it does not it could be the stat or a component in the electric heat circuit.
    Thanks for the reply.

    I forgot to mention in my original post that if I raise the setpoint 4 or 5 degrees, the auxiliary heat will kick on. I have checked that myself and the tech that came out Monday did as well.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 26, 2007, 12:51 PM
    Looks like just the thermostat. REMEMBER (write down) the colors of the wires and where they came from so you can change out to a new t-stat with little or no problems.
    Make sure you get a 2 stage heat and one stage cool heat pump thermostat.
    You can check the beginning of this board under sticky notes to help with thermostat wiring.
    Auburner's Avatar
    Auburner Posts: 9, Reputation: 1
    New Member
     
    #5

    Dec 26, 2007, 02:34 PM
    Quote Originally Posted by hvac1000
    Looks like just the thermostat. REMEMBER (write down) the colors of the wires and where they came from so you can change out to a new t-stat with little or no problems.
    Make sure you get a 2 stage heat and one stage cool heat pump thermostat.
    You can check the beginning of this board under sticky notes to help with thermostat wiring.
    I was looking at various thermostats on a web site - prothermostats.com (although I will purchase the thermostat at Lowe's or Home Depot) - and was able to read the installation instructions for the different Honeywell models up for consideration.

    In the installer instructions, there is a section where parameters have to be set inside the thermostat itself, such as "Changeover Valve (O/B)" (mine should be set to "O") and "Stage 2 Heat Cycle Rate/Auxiliary Heat Cycle Rate". A couple of questions I have that I imagine you can help me with:

    1) Are these parameters set after the thermostat is wired and the power from the main breaker is turned back on? (Or should it be done on battery before the whole system is powered?)

    2) For the "Fan Control (heating)", I presume I use the setting for "electric furnace (thermostat controls fan in heating)". Correct?

    3) For the ""Stage 2 Heat Cycle Rate/Auxiliary Heat Cycle Rate", I presume I use the setting for "electric furnace"? Correct?

    Given that I've never replaced a thermostat before (although it seems pretty straightforward), I wanted to be cautious and ask these questions to ensure I don't make a mistake.

    Thanks for all your help!

    --Paul
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Dec 26, 2007, 04:46 PM
    First go here to the honeywell site. In the lower right side you can type in the model number you are interested in. There is a bunch of info there including the wiring diagrams and a step by step instruction for your model.

    Default - Honeywell Environmental And Combustion Controls

    1 usually you can program a honeywell on batterys while sitting in a comfortable chair having a coffee.

    2 You might find that there is a setting for heat pump selection on the instructions for the fan.

    3 Yes

    Unless you are in a hurry you might want to look at a few different Honeywell thermostats.

    Catalog
    Auburner's Avatar
    Auburner Posts: 9, Reputation: 1
    New Member
     
    #7

    Dec 26, 2007, 05:07 PM
    Thanks for responding again.

    I've looked at the Honeywell site and have found quite a variety of thermostats that will apparently work with my system (2H/1C).

    I wanted to double check on the fan setting because the only two options I found on most of the models is "0" for "gas or oil furnace" and "1" for "electronic furnace", with no option for heat pump, although the models are for up to 2H/2C heat pumps.

    I hope I'm not being a bother, but can you tell me why Honeywell breaks the thermostats between do-it-yourself and professional installer models? I notice the professional models (such as the PRO or FOCUS models) seem to each handle a wider variety of heating/cooling configurations, but wonder if there is a good reason why I should stick to the DIY model or, if I were to consider a professional installer, why I would go with the professional installer models?

    From the wiring instructions I see, I don't see anything any more difficult, as long as I'm sure to get a model that handles my 2H/1C configuration.

    Thanks!

    --Paul

    Quote Originally Posted by hvac1000
    First go here to the honeywell site. In the lower right side you can type in the model number you are interested in. There is a bunch of info there including the wiring diagrams and a step by step instruction for your model.

    Default - Honeywell Environmental And Combustion Controls

    1 usually you can program a honeywell on batterys while sitting in a comfortable chair having a coffee.

    2 You might find that there is a setting for heat pump selection on the instructions for the fan.

    3 Yes

    Unless you are in a hurry you might want to look at a few different Honeywell thermostats.

    Catalog
    AC Doc's Avatar
    AC Doc Posts: 12, Reputation: 1
    New Member
     
    #8

    Dec 26, 2007, 05:19 PM
    The pro series thermostats have a program mode that has to be entered by 2 keys being pressed at the right time. Once in the program mode follow thur the codes to make sure your set them right with your system. If you have any questions lean toward the factory setting. I have a code book and can help if you need any help. You should be able to install any of them if you can follow the easy to read diagrams in their installation guide.
    AC Doc's Avatar
    AC Doc Posts: 12, Reputation: 1
    New Member
     
    #9

    Dec 26, 2007, 05:22 PM
    A local HVAC parts house should be able to sell you a Pro 8000 stat. The dehumidification one is the one I lke. This way you can see the humidity level in your house. Price around 200.00
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Dec 26, 2007, 06:22 PM
    The problem you might run into buying a thermostat at a real HVAC parts house is warranty. Since you are considered a non pro they might not want to warranty the product. Also read the fine print on the pro warranty. Many times it will say warranty void if not professionally installed or something like that. Many times they will want a bill from the HVAC company on there service invoice to you that says they installed the thermostat for you. Just a thought.
    Auburner's Avatar
    Auburner Posts: 9, Reputation: 1
    New Member
     
    #11

    Dec 26, 2007, 09:58 PM
    Quote Originally Posted by hvac1000
    The problem you might run into buying a thermostat at a real HVAC parts house is warranty. Since you are considered a non pro they might not want to warranty the product. Also read the fine print on the pro warranty. Many times it will say warranty void if not professionally installed or something like that. Many times they will want a bill from the HVAC company on there service invoice to you that says they installed the thermostat for you. Just a thought.
    I think I'm going to go with the Honeywell "RTH7400D 5-1-1 Day Universal Programmable Thermostat". I'll pick it up tomorrow and put it in.

    From looking at the wiring in my current thermostat and the wiring info I have found on-line (Honeywell's PDF file with installation instructions), this seems pretty straightforward.

    Thanks for all the help today. I'll let you know how it goes.
    Auburner's Avatar
    Auburner Posts: 9, Reputation: 1
    New Member
     
    #12

    Dec 27, 2007, 05:35 PM
    After price checking at Lowe's and Home Depot, I decided to go with the Honeywell RTH7500, 7-day programmable. It was $15.00 cheaper at Lowe's than at Home Depot and only $5.00 more than the RTH7400 (at both Lowe's and Home Depot) I had been looking at. And -- Lowe's had a deal where any purchase over $50.00 would include a $10.00 coupon good for my next purchase.

    Installation went easy and smooth. I owe thanks to Honeywell for engineering a good user interface and installation instructions, to the tech who gave me some tips when he came out the other day, and to you hvac1000. You really helped me put together the various pieces and was responsive in your answers so that I felt comfortable doing the thermostat replacement myself.

    Thanks for all the help!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #13

    Dec 27, 2007, 08:03 PM
    Glad to be of service. Happy New Year
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #14

    Dec 28, 2007, 09:58 PM
    Best advice you got was to stay away from Hunter,, haven`t see a goodone yet
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #15

    Dec 28, 2007, 10:00 PM
    Best advice you got was to stay away from Hunter,, haven`t see a good one yet
    Auburner's Avatar
    Auburner Posts: 9, Reputation: 1
    New Member
     
    #16

    Dec 29, 2007, 08:44 AM
    Quote Originally Posted by wmproop
    best advice you got was to stay away from Hunter,,,,,haven`t see a good one yet
    And I did. Got the Honeywell.

    Thanks.
    AC Doc's Avatar
    AC Doc Posts: 12, Reputation: 1
    New Member
     
    #17

    Jan 15, 2008, 05:27 PM
    Yeah so go buy a Lowe's brand hunter cheapy thermostat that does not half work. That a better Idea.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Heat Pump won't turn off [ 9 Answers ]

I have a Goodman heat pump that's 5 years old (the original heat pump installed when the home was built). Today I turned the heat up from 65 to 70, the heat pump started running (it should have since it was less than 70 degrees in the house). Problem is, it got up to 75 degrees before I noticed...

Lennox heat turn off and turn back on to work [ 2 Answers ]

I have a lennox heater I have to turn it off and turn it back on to get it to heat. What is wrong and how do I fix it.

20 yr old Lennox heat pump fan blows constantly in heat mode [ 5 Answers ]

20 year old Lennox heat pump - outside temps been 30's at night, 40's daytime UPDATE: I went outside and the unit is covered in frost on 3 sides! I've been reading on Google about frosted heat pump units and can't determine how to manually defrost it. Apparently, the auto defrost is not...

Ductless A/C with Heat Pump - Heat pump does not come on [ 1 Answers ]

Hi The A/C works great but in the morning when its cool outside and I switch on the Heat the indoor unit makes a clicking sound and the fan stays off - after about 8 minutes I switch to A/C I get a rush of ice cold air along with some mist. Seems like when I switch to heat the indoor unit...

A/C furnace running, but heat pump fan does not turn [ 1 Answers ]

Hello, I have a Lenox Elite 13 heat pump; the furnace inside the house is running. But I notice that the heat pump fan does not turn. When I go to inspect the H/pump, I hear a noice coming from the h/pump, like there is power. Someone told me that it could be my run capacitor? I removed the Run...


View more questions Search