    Need help with Thermostat wiring
    I am having trouble figuring out the wiring for a new programmable thermostat installation.

    I am replacing a RobertShaw 9420 thermostat. I bought Honeywell RTH7500D programmable thermostats to replace it because I wanted a programmable thermostat. I have central AC and a heat pump.

    The curret thermostat is wired with the following:
    Red Wire > R
    Yellow Wire > Y2
    Green Wire > G
    White Wire > W2
    Orange Wire > O
    Blue Wire > C
    There are also a brown wire and a black wire not used coming out of the wall.

    The new honeywell has the following connections:

    Conventional --- HP
    C --- C
    G --- G
    Y --- Y
    W --- O/B
    RC (jumped to R) --- RC (jumped to R)
    R --- R
    W2 --- AUX
    Y2 --- E
    --- L

    Any ideas on what wire goes to what? I can't figure out the orange wire and the blue wire and I don't know if I need the brown or the black.

    Thanks!
    Paul
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #2

    Oct 2, 2005, 07:24 AM
    How are the wires connected in the air handler/frunace? Post back with that Iand I may be able to help.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Oct 2, 2005, 08:19 PM
    I am sure I already answered this, but don't see my answer. As I said, the blue may not be needed, just cap it off.

    These W2 --- AUX
    Y2 --- E
    --- L
    Contacts may be for the thermostat to control different rates. Some of them may be for an outside temperature sensor. If the heat pump doesn't have the same labels as the thermostat, you will need to study the installation manuals for both to use the special features.
    Broncowolf's Avatar
    Broncowolf Posts: 5, Reputation: 1
    New Member
     
    #4

    Oct 3, 2005, 01:34 PM
    The only wires that connect to the air handler in the attic are the following:

    Red
    Green
    White
    Blue

    There is also a brown wire coming from the air handler that is capped off.

    The yellow and orange wires seem to come from the AC unit outside.

    I contacted Honeywell support and Robertshaw support and they don't seem to understand why the yellow wire would be connected to the Y2 terminal instead of the Y1 terminal in the current Robertshaw 9420 thermostat. Nothing is currently connected to the Y1 terminal. However, I do notice the AC unit outside blowing when called upon.

    And thanks, Labman, I noticed you did respond to another posting I did. I should have cancelled that other posting because I think I put it up in the wrong forum and I also had some fact wrong in that one.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Oct 3, 2005, 04:02 PM
    Not all systems are set up to use different heating and cooling rates. You may not need the orange and black wires at the thermostat. If the cooling works now, and the heat does when you need it, I would leave things alone. If the heat doesn't work, try the W1 terminal on the thermostat.

    And thanks for reassuring me I had responded to the other thread.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

HELP! Thermostat Wiring [ 3 Answers ]

We just bought an older house and are in the process of replacing 1960's wood paneling with drywall. The thermostat had been "painted" onto the paneling (many times over). After I removed the screws, I had to pry the t'stat away from the wall, which caused the wires to become dislodged from their...

Wiring a new thermostat [ 1 Answers ]

How do I wire a White-Rogers thermostat (Model#1F82-261) to a Goodman Heat Pump (Model#CPKE30-18). I know red wire goes goes to "R" terminal, green wire goes to "G" teminal but I need to know about the white, the yellow, the light blue, and the brown wire. My heat pump is a single stage cooling and...

Thermostat wiring [ 1 Answers ]

I just bought a Hunter programmable model 44260 and trying to replace an old Honeywell for my heat and air system. The Hunter directions don't talk about a W1 & W2 terminals that the old one has.The Honeywell is wired like this - White wire on W1 ,blue onW2, green on the G, Red on Rc & Rh which are...

Thermostat wiring [ 3 Answers ]

Hi all, great site! My problem is that we only have 3 wires coming up to our thermostat. We are installing central air and I was wondering if it is possible to wire the thermostat with only 3 wires?? Thanks :D

Thermostat wiring help [ 1 Answers ]

I'm installing a new thermostat. The old one just controlled heat, and my idiot brother-in-law (who works for trane btw) somehow rigged it to work the heat and air. The wiring for the heat was pretty self explanitory, but the wires to the air are not labeled and I have no idea which is which. Can...