    Heil sp80 gas settings
    Good Day:

    Our furnace is a Heil SP80 model #NU65100BFB2, 100K BTU output, converted to LP gas. The main gas valve failed (Honeywell SV9500M 2682, converted, dead solenoid)

    We have just put in a new main gas valve (Honeywell SV9501 M2056), and personally put in the gas conversion from NG to LP. The output pressure on the manifold is exactly 2.5" WC (as reqested in the new literature for LP), confirmed the jets on the manifold as #54 LP orifice. We used a $4000 NIST calibrated Digitron to check the pressure through the enitre heating cycle.

    Whats getting me a little concerned is that the flame (nice blue, no yellow, no visible sooting) across the manifold outlet to the heat exchanger is considerably larger than the original valve. The jet is the size of the shell on the HX, and a ribbon of flame is seen across the outlet of the manifold. THere does not seem to be any negative reaction, but the flame characteristics are jsut differnt than before. The unit does not overheat, and seems to cycle properly.

    We bought the building with the furnace installed and have no literature. I am not sure if the unit was operating properly when we moved in.

    Is there another way to insure that this is the correct set up? Is the 2.5"WC the right value, or will this get adjusted lower for particular instances? I am an oil guy, first time around with a propane unit. Does anybody know where to get an old copy of the installation manuals?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 19, 2008, 11:29 AM
    Make sure the pressure is set to the furnace label and not the gas valve. Propane as well as natural gas can be fired at different pressures so you have to use the design pressure for the unit you are working on. It will be on the furnace label.
    john public's Avatar
    john public Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 20, 2008, 05:10 AM
    Quote Originally Posted by john public
    Good Day:

    Our furnace is a Heil SP80 model #NU65100BFB2, 100K btu output, converted to LP gas. The main gas valve failed (Honeywell SV9500M 2682, converted, dead solenoid)

    We have just put in a new main gas valve (Honeywell SV9501 M2056), and personally put in the gas conversion from NG to LP. The output pressure on the manifold is exactly 2.5" WC (as reqested in the new literature for LP), confirmed the jets on the manifold as #54 LP orifice. We used a $4000 NIST calibrated Digitron to check the pressure through the enitre heating cycle.

    Whats getting me a little concerned is that the flame (nice blue, no yellow, no visible sooting) across the manifold outlet to the heat exchanger is considerably larger than the original valve. The jet is the size of the shell on the HX, and a ribbon of flame is seen across the outlet of the manifold. THere does not seem to be any negative reaction, but the flame characteristics are jsut differnt than before. The unit does not overheat, and seems to cycle properly.

    We bought the building with the furnace installed and have no literature. I am not sure if the unit was operating properly when we moved in.

    Is there another way to insure that this is the correct set up? Is the 2.5"WC the right value, or will this get adjusted lower for particualr instances? I am an oil guy, first time around with a propane unit. Does anybody know where to get an old copy of the installation manuals?
    Thanks for the headsup. The plate on the furnace is rated in NG, and has a 3.5 kPA rating. The valve was also rated at 3.5 kPA for NG and 2.5 kPA for LP converted, so I assumed that the furnace was also compatible at 2.5 kPA LP. Bad ssumption?
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #4

    Mar 20, 2008, 05:16 AM
    Your model number is not correct... kindly re-check and post it for us. NOTE: on ICP... heil / tempstar furnaces the LP gas pressure is never 2.5 inches of water... if you run it that low you will soot up the unit!! NOTE: that is why I wonder if you converted the unit correctly ! The conversion kit comes with a low pressure LP safety switch that you install before the gas valve to shut down the unit if it sees LOW LP feed from the tank.. . the ID plate will list the Nat. gas pressure at 3.5 inches of WC... LP is usually 10 inches on the manifold side. Post the correct model number and I check the original specs for the unit...
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #5

    Mar 20, 2008, 05:38 AM
    Your model number must be a NUG5100BFB2 (not a (NU6**) the LP conversion kit did not come with the low pressure safety switch... the # 54 orfices is correct for LP... with a factory install manual spec. of 10 inches of water col. On the manifold side, and a min. LP feed pressure from the LP tank while running of 11 inches of water col...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Having troubles with heil gas furnace [ 2 Answers ]

I have a heil forced air heating furnace that is going on and off and will not stay on to come up to temperature. It will not burn for more that a minute before it cuts off again. It was working fine just a week ago and now it is doing this. Would you have any idea of what may be wrong and what...

Heil SP80 furnace malfunction - possibly the valve [ 3 Answers ]

The electric igniter does not ignite when the furnace should. The blower works fine, and is the first thing that goes on when the furnace is on for a heat. When I press on the wiring connector that goes into the valve the igniter then gets red hot and then the fire begins. I was wondering if...

Heil gas heating system [ 1 Answers ]

We have a Heil gas heating system and we lighted the pilot and when we turned the temp up it kicked in but it felt like the fan did not come on

Heil gas furnace won't blow [ 2 Answers ]

I have a Heil heat/air gas pack(forced air) unit. It's about 20 years old, but it's been a great one. When I flip the t-stat to HEAT and AUTO I hear the unit outside firing up and I can see heat rising out of the vent, but the blower won't come on to push heat inside my house. When I turn the...

Heil 92% H9MPDO75F12B Gas Furnace [ 1 Answers ]

I had a Heil Gas Furnace installed and from the first day I notice that when the blower came on the air was on the cool side. After about 1 to 2 minutes the air became a little bit warmer but never got hot. My question is this normal or do I have a problem? Please let me know as soon as possible so...


View more questions Search