Jan 17, 2006, 04:42 PM
|
|
Makeup Combustion Air for furnace
I have just finished my basement and my furnace is now in a room about 20 x 20. I had installed double doors (solid not vented) to enter the room which is also being used for storage.
My question is do I need to add some kind of makeup air for combustion by installing a grill in the wall? How do I know how large I need? Is there a way to calculate this? The heater is a 125,000 BTU york furnace about 2 years old.
Thanks for any help.
|
|
|
Senior Member
|
|
Jan 17, 2006, 09:31 PM
|
|
Next to the exhaust vent on the furnace, is there another vent connection? If so this is where a fresh-air vent pipe can be installed and piped to the exterior.
Air from with-in a building
"If the volume of space is greater than 50 cubic feet per 1,000 BTU/h....normal infiltration shall be regarded as adequate...
If not, 2 openings in a wall, with one 12" from the top & one 12" from the bottom. Each opening shall have a free area equal to min. 1" square inch per 1,000 BTU/h input rating of the appliance installed but not less than 100 sqr. Inches." (Internation Res. Code, section M1702.1 M1702.2)
|
|
|
Uber Member
|
|
Jan 17, 2006, 09:42 PM
|
|
If you have an installation manual for your furnace, it should tell. If not, go with the above rules. Those rules assume average construction. I actually tightened my crawl space up so tight, I had to add a vent for the furnace. I used the space between 2 joists as a duct ending it about a foot short of the furnace since the furnace was not set up for a duct.
|
|
|
New Member
|
|
Jan 18, 2006, 05:35 AM
|
|
Great - Thanks for the info, that's what I was looking for!
|
|
|
Full Member
|
|
Jan 18, 2006, 09:26 AM
|
|
Originally Posted by jimd60
I have just finished my basement and my furnace is now in a room about 20 x 20. I had installed double doors (solid not vented) to enter the room which is also being used for storage.
My question is do I need to add some kind of makeup air for combustion by installing a grill in the wall? How do I know how large I need? Is there a way to calculate this? The heater is a 125,000 btu york furnace about 2 years old.
Thanks for any help.
125000 btu= 1.25 cubic ft... 1 cubic of natural gas require 10 cubic ft of air for a complete combustion... generally they use 50% excess of air... the min.excess air is 25%
|
|
|
Heating & Air Conditioning Expert
|
|
Jan 18, 2006, 12:46 PM
|
|
If you want to make it real simple for yourself just add a vent to the supply and lock it open. The burner will draw combustion air from the register/duct system and when the blower is running there will be more air than needed. Code actually call for combustion air to be from a source that is 50% hi and 50% low is a enclosed room.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Where do you buy your makeup?
[ 3 Answers ]
Hello,
I am new to this site and I am trying to get stores to sell my fiance's aunt's new makeup line called about face by Pamela John. It is a mineral-based makeup line.
The question I have for you all is where do you normally buy your makeup products? (department store, salon, independent...
Mineral Makeup?
[ 2 Answers ]
I just recently heard about this. What do you know about it and what brands are best? Thanks
Need to replace combustion air blower
[ 2 Answers ]
Hi,
I have a Comfort Air furnace. The "Fasco" combustion air blower is making a noise when starting up and running.
I want to replace the whole unit.
Does anyone know of a reputable online dealer to buy it from?
Cooling tower evaporation, blowdown, makeup and cycles
[ 0 Answers ]
Here are the governing relationships for the makeup flow rate, the evaporation and windage losses, the draw-off rate, and the concentration cycles in an evaporative cooling tower system:
http://www.air-dispersion.com/CoolingTower.gif
M = Make-up water in gal/min
C = Circulating water in...
Combustion Air Blower makes noise.
[ 3 Answers ]
Hi all,
I have a 4 and 1/2 year old ComfortMaker furnace. The combustion air blower started making a rumbling noise while starting and stopping and continues to vibrate while running.
I had a heating & cooling service look at it. $65 just to show up.
Without taking anything apart he said...
View more questions
Search
|