    Air conditioning unit tripping circuit breaker
    I have a 30 amp circuit breaker to my central air unit. It worked just fine last summer. This summer it started tripping the breaker. I changed the contacts just in case that was the problem. This worked for a couple months. Now, it is tripping again. Could it be the breaker is worn out? Please help. Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 27, 2009, 10:44 AM
    I changed the contacts just in case that was the problem.

    What are contacts? There is a item called a contactor in the outside unit is that what you replaced?

    Many items can cause a circuit breaker to trip on over current.

    A circuit breaker will weaken if it trips and has to be reset too much. The bimetal in the breaker weakens and causes this.

    The unit outside could be

    Overcharged with refrigerant.

    Coils dirty

    Out of range run capacitor.

    Unit needs a hard start kit

    Loose or damaged wiring anywhere from the unit to the house panel.

    Short cycling

    There are a few more but I think you get the idea.

    You may have to get a on site professional who has the proper tools to figure it out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Circuit breaker keep tripping [ 4 Answers ]

Hi, The problem is that the breaker trips and I cannot reset it, but after a few hours sometimes I can reset it but then it will trip again then when I try to reset it the breaker arc and woun't reset. Help!!

AC Circuit Breaker Tripping [ 4 Answers ]

My Trane AHU/CU cools great except that twice in the last 2 weeks the circuit breaker has tripped. Both times I have noticed it has got hotter in the house, I go out in the garage and the AHU Blower is blowing but the CU is not running. I check the panel and the circuit breaker is tripped. I reset...

Circuit Breaker Tripping [ 1 Answers ]

We have installed a electrical box on the home that houses a 20 amp fuse w:gfi off the meter, then ran the wires to a outdoor box w: a gfi plug & a on/off switch. Seems to be wired correctly, but the 20 amp fuse keeps tripping. Thank You in Advance for any help, Michael

Outside unit is tripping the circuit breaker [ 5 Answers ]

My Outside AC , which is a pretty old unit( 15+) recently started tripping the circuit breaker. If I go and turn the circuit breaker back on the unit will run for about five minutes then trip the circuit breaker again. Is it time to replace the unit? My AC repair guy did tell us last summer...