    Carrier or Honeywell Zone System?
    Hey all! I have a 2700sqft home that is two stories half of that is upstairs and half down. I have a 4 year old 5 ton all in one AC/Heat unit and only one return in the house which is downstairs.

    I have been getting estimates on getting a second return put in upstairs along with a zone system so that I can control the temperature upstairs better. All in all it sounds freaking fantastic for not a fortune of money (although its still expensive).

    Of my best bids one uses Honeywell and a little higher bid uses Carrier.
    The Honeywell one they said only has open and closed states on the dampeners and the two thermostats are non-programmable.
    The Carrier one they said each dampener has 8 levels of dampening for much better controls and both the up and down thermostats will be programmable along with giving me addition information about the air flow, temps, etc.

    Is the Carrirer worth the extra money?
    Are these both good brands?
    Does anyone have the manufacturer websites for them?
    Are there any brands that I should make sure to stear clear of?
    All information is appretiated!

    Thanks!
    --Cameron
    shunned's Avatar
    shunned Posts: 268, Reputation: 20
    Full Member
     
    #2

    Jul 19, 2006, 05:54 PM
    Sounds like the carrier guy is talking about VAV (variable air volume) boxes. Honywell can install them too, just ask. They do afford you more control.
    I think they are about the same in quality, as I've not heard anything too badly or either one.
    Magicman's Avatar
    Magicman Posts: 3, Reputation: 2
    New Member
     
    #3

    Aug 2, 2006, 08:48 AM
    If you install only one return upstairs, lets say in the hallway... each bedroom will have hot air trapped in them, especially if you keep the door shut.

    You can either branch return ducts into each bedroom (never return air from bathrooms, laundry rooms, or kitchens)... or, you could simply put one large return in the hallway and install "back to back" grills above the bedroom doors. Basically, they are just an open hole above the door, disguised with a grill on each side, to allow the return in the hallway to suck the hot air out of each bedroom.

    I don't know very much about the various zoning systems, but I expect that all of them will eventually be problematic. Its like anything else, the more complex you make a system, the more there is to break down.

    Best of luck to you.


    Magicman

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Evolution (carrier infinity) Control and Honeywell Fresh Air Vent. [ 2 Answers ]

I have an Bryant Evolution system installed. This is the same as a Carrier Infinity system. This consists of a 355MAV furnace, a 598B a/c And SYSTXBBUID01 Evolution control. Also installed in this system is a Honeywell Y8150 ventilator and a Honeywell HE440 steam humidifier. The...

Zone valve problem [ 5 Answers ]

Zone valve for upstairs will not open. Already replaced thermostat. The only time I have heat upstairs is when the valve in manually opened and the downstairs heat kicks on. Any help or advice would be great! Thank you.

Zone valves [ 2 Answers ]

Looking for a wiring diagram for a new dunkirk boiler . Just the diagram for the 3 zone valves. Company says that the boiler transformer is enough to run three zones ( 24v) . Or do I need to add transformer. Just can't figure out the wiring from one zone valve to another. Contacts on each zone are...

Can I use parallel thermostats in a 1-zone system? [ 3 Answers ]

Bought an old 3-storey house in Maine, heated with gas forced-hotwater radiators. There is only 1 zone, with the thermostat in a 1st floor front room with little traffic and away from any radiator. When the t'stat calls for heat, it takes so long for it to register at the t'stat site, that the...

Wiring a 2nd zone [ 1 Answers ]

Central a/c is all set up on my finished basement as a 2nd zone. In the upstairs hall closet, I can see a large round pipe running down from the attic to the basement. Ceiling ductwork and vents in the basement are all connected to it. There is a programmable thermostat in the basement as well. The...


View more questions Search