Old Dec 4, 2007, 06:56 PM
johnlfaz
New Member
johnlfaz is offline
 
Join Date: Dec 2007
Location: Lincoln NE
Posts: 2
johnlfaz See this member's comment history on his/her Profile page.
sub panel generator input lines required

Main and sub panels installed by electrician. Generator input circuit breakers installation was incomplete having no input lines to two 60 amp breakers. Connecting the generator to the sub panel via two 110v wires will power the well put but will not provide enough power to run 4 additional power requirements i.e. frig, rec room, etc. How do I run additional wires, add more breakers without shorting or compromising the sub panel.

Thanks

Reply With Quote
 
     

Answers
 
 
Old Dec 4, 2007, 08:18 PM   #2  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
Very confused here. Can't follow. Can we assume:

The sub-panel is just for the "critical loads"?
The system uses a manual transfer switch described below.
The sub-panel has an interlocked main breaker and generator breaker so that both can't be on at the same time?
What's the generator capacity and voltage?
Is it connected all the time?
How many spaces are used/available in the sub-panel?

You realize that sum of the breaker sizes don't mean much. You can have 100 amps of labeled breakers and a 60 amp panel.

In this sort of installation, you need to be aware of the connected loads, not the breaker size. You then must ensure that the connected loads don't trip the generator breaker. So, you might have to do without well water when the fridges need to be on.

Things don't make sense because you say two 60 amp breakers. This is one 60 amp double pole 220 V breaker. It has a bar between the two breakers, so if one trips, the other one does too. This is a lot of generator capacity. It's extremely unlikely that a frig, a few lights and a well pump would exceed 120 Amps of 120V unless your counting the values on the breakers themselves.

Comments on this post
johnlfaz agrees: Ongoing, but individual is very knowledgable and helpful.
  Reply With Quote
 
     
 
 
Old Dec 4, 2007, 09:50 PM   #3  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
Moved reply to forum:

Yes sub panel for critical loads
Understand manual transfer switch and need and no both can not be
turned on at once
generator capacity is 5000w voltage is one 220v, two standard 110 and
one 110 3 prong
no it is not connected all the time. only to be used as backup power
spaces used: two utility wires in from main breaker box each to a 60
amp breaker
two 60 amp breaker currently not used but meant for generator power
4 outputs wired, top two for 220 to well pump, the lower 4 for
individual circuits.
Yes, that's what I need to know, how to wire "IN" more power than setup
current allows with only two input locations.
As for exceeding generator output, well pump is 220 itself, furnace,
frig and entertainment center not much alone but note that generator
output max is 30amps. That's what I'm trying not to exceed by running only
one cord from generator to transfer box. Hope you can help. Thanks
John
  Reply With Quote
 
     
 
 
Old Dec 4, 2007, 09:51 PM   #4  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
John:
If you use "Go Advanced" you can post photo's directly to the forum.
  Reply With Quote
 
     
 
 
Old Dec 4, 2007, 10:13 PM   #5  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
5000/240 is about 20 AMPS. That should be the size of the generator transfer breaker. The utility side can be 60 amps. These two breakers must be interlocked.

Power from the generator should be wired to a generator input connector outside. You will then take the 240 outlet which should have 4 wires. One L1, L2, N and ground. L1, L2 will go to the 20 amp generator input breaker. N and ground will connect to the sub-panel. The sub panel should have an isolated neutral bar and a separate ground bar. The Neutral to Ground connection in the generator needs to be removed.

What this means is that when under utility power, 60 amps are avalable to the critical loads.

When power fails, you move the 60 AMP breaker to off. Turn off all the breakers in the sub-panel. The move the 20 amp transfer breaker to on.

Now, you select which circuits you want on generator power.

Does this make any sense?
  Reply With Quote
 
     
 
 
Old Dec 4, 2007, 10:26 PM   #6  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
The interlocked breakers should really be in the sub-panel. The main breaker 60 A in the sub-panel would be interlocked with a 20 amp transfer breaker. It would be fed with a 60 amp breaker in the main panel.

The other way to wire it would be to have the main breaker in the main panel interlocked to a 20 amp transfer breaker, but in this case all loads can be operated from the generator and all of the breakers but the 20 amp transfer breaker needs to be off. In this case the generator wires go to the main panel.
  Reply With Quote
 
     
 
 
Old Dec 5, 2007, 11:51 AM   #7  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
Again moved:

Simple,
I think I have enough information to go ahead and run the wire I need
to the sub-panel. What I was trying to do was run multiple connections
from the generator to the sub-panel in order to power the applicance I
consider criticle. But from what you stated, the generator is rated at
20-30 amps. That being the case, if I try and tap into multple
outlets, I will quickly exceed the manufactures capacities. So I'll just run
one connection from the generator to the sub-panel. Just one more
question if you please. Since I will be connecting to the 220 4 lead outlet,
does it matter to the 220 well pump which hot wire goes to which lead?
Can I unintentionally have them backwards? Sorry for all the questions
just trying to save a few bucks here. Besides, they didn't teach us
this in avionics school.
John
  Reply With Quote
 
     
 
 
Old Dec 5, 2007, 12:21 PM   #8  
Engineering & Electronics Expert
KeepItSimpleStupid is offline
 
KeepItSimpleStupid's Avatar
 
Join Date: Aug 2007
Posts: 9,334
KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.KeepItSimpleStupid See this member's comment history on his/her Profile page.
X and Y are interchangeable with red and black. You might try keeping them the same as the generator color codes for the coresponding terminals.

W is white and G is ground/green/bare.

The well pump doesn't matter.

The neutral conductor carries the difference of currents between L1 and L2 or X and Y.
It also makes some sense to try to distribute the 120 loads such that L1 and L2 will be symetrically loaded with devices that you may have on together if possible.

Check your generator instructions to see if you can have all 5000 W at 120 V. Then it wouln't matter.
  Reply With Quote
 
     

Your Answer
Email me when someone replies to my answer
Join Login





Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

 
Similar Sponsors


Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page

Similar Threads
tangent lines & secant lines
(3 replies)
Breaker size in main panel to support sub panel?
(7 replies)
200 AMP Service panel to 200Amp Sub Panel
(1 replies)
Main Circuit Panel to Branch Panel?
(1 replies)
Kenmore Elite Dryer Toe panel - how to get panel OFF!
(3 replies)

Search this Thread

Advanced Search

Bookmarks

Sponsors



Copyright ©2003 - 2009, Ask Me Help Desk.
All times are GMT -8. The time now is 02:47 PM.