    I have a 500 Amp service panel. One 250 AMP breaker is being used for the house and the other 250AMP breaker is not being used.

    I would like to connect to the unused 250AMP breaker and run 240V to a sub panel 244 feet away where I will have a hot tub 50AMPS and a 30AMP draw for a trailer or a 100 AMP total draw at the sub panel.

    What gauge of wire will I need and what size of conduit will I need to run it underground?

    Thank you,
    Buddy1
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 6, 2007, 03:46 PM
    Use 3-#250 MCM XHHW and 1#2 XHHW in 3 " PVC Sch 40 PVC conduit.

    Are you sure a 250 amp breaker in a 500 amp panel? Very odd size.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

200 Amp Service Panel with 60 Amp Main Breakers [ 26 Answers ]

I was told when we purchased our house that it had 200 Amp service which it appears to be; however, the top of each bus bars only has 60 Amp breakers for the Main shut offs. Is this normal? Each bus bar is connected to a hot wire (one red and one black) and then the two 60 amp breakers are...

100 amp sub-panel [ 3 Answers ]

Can I put a 100 amp sub-panel in my attic? My attic has pull down stairs and is unfinished. I was hoping I can put a sub in my attic to make it easier for numerous runs I have to do on the second floor. I want to be up to code and do not want any issues with homeowners insurance. Thanks, mike

125 amp sub panel [ 5 Answers ]

What size wire do I need to pull for a 125 amp sub panel. Thank you