    Main Panel to Sub Panel
    I currently have a CH MBE4040B200BTS Meter main panel on my pump house drawing only power to run booster and well pumps, here is what I wish to do:
    Add a CH BRS225 (feed thru) to a CH BR4040B200 Main Breaker sub panel for my shop. Both panels are only 200 amp service, I will not be running more than the compressor ans 1 other item at a time (aside from lighting). Does anyone forsee a problem with my thoughts? I have a PDF file of my shop elec drawing and the hookup.

    Thanks,
    Bob
    Attached Images
  1. File Type: pdf Pump To Shop Elect.pdf (11.8 KB, 270 views)
  2. File Type: pdf Shop Electrical layout.pdf (40.2 KB, 585 views)
  3. tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 1, 2007, 11:35 AM
    I see no problem with it, looks like a good use of the 200 amp service now just for the pump.

    You may want to consider using #4/0 Aluminum instead of the #2/0 copper, one to save a ton of cash, but more importantly reduce voltage drop. If you have a 100 amp load in the shop, the #2/0 will produce a 10 volt drop, which is more than the recommended 3%. If you use #4/0 Al for the same load and distance, the volts dropped will be about 3.5 volts, well below the 3%.

    The feeder to the subpanel should be 4 wire, and at least one ground rod will be needed to ground the equipment ground at the subpanel. Keep the neutral and equipment ground separated at the subpanel.

    I hope this helps, do not hestitate to get back with any other comments or questions.
    BSelff's Avatar
    BSelff Posts: 11, Reputation: 1
    New Member
     
    #3

    May 1, 2007, 11:41 AM
    I have had them install a Eufer (ground bar attached to the rebar in the slab) in the workshop for grounding it separately.

    Bob

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...

Main panel as subpanel [ 2 Answers ]

Hello: I stumbled across your forum and found a question that was close to mine, but have a more detailed query. I am wiring a shop/apartment. The building has a 200 amp service panel. The main loads (a/c, range) and dedicated loads (fridge, smoke detectors, etc) are branch circuits on the main...

Main Services Panel [ 1 Answers ]

Do`s Anyone Know Were To Find A Two Meter Pedastole Pannel "main Service' So Two Dwellings Can Have There Own Meter. You Know Power Comes From The Pole Then To The Pedastole And Then To Two Mobile Homes

Sub Panel with a main in Position 2,4, 6 [ 2 Answers ]

My question concerns panel boards where the main breaker takes up two or three positions on the panel board. If I use a main in position 2,4,6 the corresponding positions 1,3,5 have to be left blank according to code.


View more questions Search