    Can I change a 30 amp breaker to 2, 15 amp breakers
    This is an unused 30 amp no power to it.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Dec 25, 2012, 08:16 AM
    You can remove a breaker and use that spot for almost anything.

    Your post is confusing. What are you looking to do exactly?
    ptodryk's Avatar
    ptodryk Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 25, 2012, 08:35 AM
    I am looking to add 2 outlets and a light in an upstairs bathroom and I don't want to overload any other circuits. So I am hoping that I could use the unused 30 amp spot to put in a couple of 15's and have one 15 for a spare. That way I'll have all NEW wiring going to the panel.
    ptodryk's Avatar
    ptodryk Posts: 3, Reputation: 1
    New Member
     
    #4

    Dec 25, 2012, 08:42 AM
    Sorry, I should say nothing is wired to the 30 amp but there is power to it.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Dec 25, 2012, 08:51 AM
    Do you understand your question, because I do not. Do you have any training in electricity or electrical safety?

    To begin with is this 30 amp breaker a single pole or double pole breaker? If it is a double breaker, then NO! If this is a two slot breaker, then the problem with using two separate 15 amp circuits would be that you create a "Multiwire Branch Circuit" This would then require that the Neutral be shared by both of the 15 amp circuits, If you do not do this correctly, then any thing you plug into the circuit will almost immediately fry.

    Next, a breaker draws power from its connection point on the panelboard and in turn supplies the power to its circuit by the conductor connected to it.

    So if you see a breaker, without a conductor does not mean the breaker is not hot. I've seen panelboeards where spare breakers were used instead of blanks to keep the front cover free from open holes.

    Never understood that one either, use a $30 breaker instead of a $0,20 plastic cover.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Dec 25, 2012, 10:00 AM
    I am looking to add 2 outlets and a light in an upstairs bathroom and I don't want to overload any other circuits. So I am hoping that I could use the unused 30 amp spot to put in a couple of 15's and have one 15 for a spare. That way I'll have all NEW wiring going to the panel.
    OK, so you just want to use the space provided by removing a double pole 30A breaker.

    Absolutely fine. Consider that space like any other empty breaker space in the panel.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #7

    Dec 26, 2012, 07:03 PM
    Yes you can, you could put in any size breaker or breakers you want. Just a note, make sure the outlet in the Bathroom is a GFCI.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Change 15 amp breaker to 20 amp [ 12 Answers ]

I'm rewiring my entire house and I have a 125amp panel. My house is small, about 800sqft but I'm finishing my basement then the area will be 1,600sqft. I don't have any 20amp breakers in the panel and I want to install a central A/C. Can I replace any of those 15amp breakers for 20amp if I use #12...

Change 15 amp breaker to 20 amp [ 8 Answers ]

Hi, I've got a very small basement workshop where I have a 1 1/2 hp tablesaw (15 amp) and a 1 1/2 hp dust collector (15 amp). I've got outlets in the basement on two separate circuits. Both circuits have 15 amp circuit breakers. It seems that either of those machines will draw a bit more than...

Breaker Box Amps rating & Number of breakers installed [ 1 Answers ]

I have a question in regards to amps allowed in a breaker box. My breaker box has a label stating that the box has a maximum load of 200 amps, but that it is convertible. I really don't know what the convertible part means. If I look at the breakers installed, these add way more than 200 amps. ...