    320 amp meter socket line wire
    Upgrading a farm elect service. He wants 320 Amp.
    I have been looking at a 320 amp pedistal main with 2 200 amp breakers.
    Can I get one that will take 4 breakers 2 200 amp 2 150 amp?
    Thnking of installing the pedistal on utiliity pole and then underground to branches. 3 buildings 1 corn drying station. No milking cows on farm. It is now and has been operating on 200 amp with a lot of 200 amp bugging going on. Not quality work!
    Any other sugestions are welcome. Little experence with branch curcuits like this.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 6, 2010, 12:42 PM
    Cannot load a 320 amp service with 2-200 and 2-150 amp breakers, the max I have seen is 2- 200 amp.

    All feeders from the meter pedestal with main breakers need to be 4 wire.

    Ground rods are needed to ground the equipment ground bar at each separate building/panel. Keep neutrals separate from equipment grounding.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring 2 Gang Meter Socket w/ 100 & 200 Amp Meters [ 10 Answers ]

Hello, Are you allowed to use a 2 gang 200 amp meter socket to feed (1) 200 AMP panel and (1) 100 AMP panel, or do all meters in same enclosure have to be the same (200 AMP)? If the above is allowed: What size wire would I need from weather head to meter socket? Would I then run...

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

320 amp meter [ 1 Answers ]

I set 2- 2oo amp main breaker panels in a house and ran 4/0 4 wire to the meter base which is 320 amp meter base the panel upstairs is about 30 ft away from the meter will I need another disconnect at the meter for that panel

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

320 amp meter socket line wire [ 10 Answers ]

I am installing a new service with two meter panels. One 320 amp meter socket and one 200 amp meter socket. The 320 amp is a 400 amp socket panel with a disconect (two 200 amp breakers). What size of line in from the transformer wire do I need? It's a typical 3 wire, single phase service. Does...


View more questions Search