    Having new 100amp meter installed professionally,but I am burying wire to the building which is 125' from where meter is mounted. Will I have to upsize the size of wire because of the distance? I also intend to enclose in conduit, so I'm not worried about using "U" coded wire
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 29, 2006, 03:27 PM
    For a 100 amp service at this length I would use #2 copper or #1 aluminum.
    If using continuous conduit, you can use THWN or XHHW insulation.
    Riders3627's Avatar
    Riders3627 Posts: 6, Reputation: 1
    New Member
     
    #3

    Jan 11, 2012, 05:31 PM
    2*k*i*l/cmil that is the formula for Voltage Drop

    2 Being the common
    K Being the type wire you are using (12.9 Copper 22.4 AL)
    I For ampacity (How many amps to deliver)
    L Length of the wire being pulled ( be sure to measure the route of the wire)
    Cmil is the size of the wire being used located in the back of the NEC in Annex C

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical entrance cable [ 7 Answers ]

We have been advised by our insurance co. to replace the electrical entrance cable... does anyone know exactly what that takes... what materials,etc... thanks..

Service entrance cable [ 23 Answers ]

I am re-wiring an old house. It is a small 2 bedroom, 1 bath house. We put in a 200 amp service and need to run a service entrance cable about 20 -25 ft to the inside breaker panel. My question is how big of a gauge wire should we run for the service entance cable. #? 3 conductor with ground in...

Entrance Cable [ 4 Answers ]

I am putting in a new electric service in my house and wanted to know what size wire I need for a 200 amp service

Entrance cable [ 4 Answers ]

How do I cover the electrical service entrance cable attached to the side of my house? What do I use? The original covering has worn out in spots, exposing wires beneath. Also is this something a dummy can do?

Service entrance [ 5 Answers ]

Can someone tell me how to find out what the amp rating of a service to a house is . The fuse box is old with edison base fuses, but the weather head and pipe to the meter cradel looks newer want to change to beaker panel Not sure what size


View more questions Search