    Wire gauge
    I need to know the wire gauge to run an above ground water pump. The voltage will be 220 volts. The pump states max. amps 26, and the length of wire run is 70 feet. Thank you. Matt
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 19, 2008, 01:05 PM
    There is no longer a 220 VAC drop. It is now 240 VAC.

    Assumptions:

    Continuous load (Power on for more than 3 consecutive hours).
    Copper conductors.
    Temperature not to exceed 86 degrees (F).
    Direct bury cable (UF 86 degrees (F)).

    You will need a dual pole 30 AMP Circuit breaker.
    70 ft. of #10/2 AWG UF (60 celsius) cable.

    That will deliver 235.5 VAC @ 30 amps to your pump.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Aug 19, 2008, 01:41 PM
    10/3 cable 30 amp breaker
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Aug 19, 2008, 01:54 PM
    Hank,

    Thanks for the quick clarification. I corrected my typo.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Aug 19, 2008, 02:43 PM
    A 26 amp load would require a 40A breaker and at least #8CU wire.

    The max continuous load for a 30A circuit and #10 wire would be 24 amps.

    Also, "3-wire" would be wasteful. There is NO need for a neutral run to this straight 240v load. 8/2 cable would be fine.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Aug 19, 2008, 02:56 PM
    Stan,

    Why? #8. A 30 amp breaker into a known 26 amp load is rated correctly.

    Did you make the change because multiplying 26 amps by 1.25 (continuous on percentage) yields 32.5 amps? In which case, you would need to use #8/2 with a 40 amp breaker.

    Odd, the wire size calculator I used did not pick up the continuous amperage change. Maybe I should go back to using pencil and paper.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Aug 19, 2008, 03:24 PM
    I think Stan did it for the distance, and the Load. The motor will love it.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Aug 19, 2008, 03:51 PM
    I did it for the continuous load as Don suggests. The OP simply says water pump.
    This could be anything, so we assume continuous load.

    26x125%=32.50A
    grandma-tlc's Avatar
    grandma-tlc Posts: 13, Reputation: 1
    New Member
     
    #9

    Aug 19, 2008, 05:12 PM
    I may not have given enough information. The water pump is 2 HP and feeds to a large pressure tank. The pump runs at the most for about 15 min.at a time to bring up the pressure. I am sorry I didn't give enough info in my question. Also, if I use 2 wires how do I ground the motor? Mabey a ground rod?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #10

    Aug 19, 2008, 05:16 PM
    Is that 26 amps at 240v or 120v

    10-2 means 2 conductors, the ground is not a conductor, therefore 10-2 will have 3 wires, 2 conductors and a ground wire.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Aug 19, 2008, 05:39 PM
    You will need to pull a #10 for ground.
    grandma-tlc's Avatar
    grandma-tlc Posts: 13, Reputation: 1
    New Member
     
    #12

    Aug 19, 2008, 06:07 PM
    That is 26 amps at 249 volts
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Aug 19, 2008, 06:13 PM
    Quote Originally Posted by grandma-tlc
    That is 26 amps at 249 volts
    HUH??

    Grandma, are you also shorey?
    grandma-tlc's Avatar
    grandma-tlc Posts: 13, Reputation: 1
    New Member
     
    #14

    Aug 19, 2008, 06:24 PM
    Yes I am using my wife's computer. I also missed a key. It's 240 Volts not 249. MY computer took a time out. Thanks.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #15

    Aug 19, 2008, 06:26 PM
    240v makes sense.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #16

    Aug 19, 2008, 10:57 PM
    Is there more info on the motor nameplate than you gave? Can the motor be run at either 120 or 240?

    240V 26A for a 2hp motor just strikes me as odd. It seems like twice the current that it should be.
    shorey01's Avatar
    shorey01 Posts: 6, Reputation: 2
    New Member
     
    #17

    Aug 20, 2008, 07:30 AM
    The nameplate shows amps as 26/13 so it can run at 120v or 240v.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #18

    Aug 20, 2008, 09:30 AM
    Then that's 13 amps at 240 volts. At 125% for motor load you are back to the 10/2 cable.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #19

    Aug 20, 2008, 11:14 AM
    430.6(A)(1) says that if a motor is marked with it's horsepower then Table 430.248 shall be used to determine ampacity instead of the nameplate. By the table you have 12A and at 125% of that you have 15A.

    Since there is a condition that would allow this motor to run continuously the circuit needs to be sized to be loaded at no more than 80% so a 20 amp breaker is required. I'd probably still run the 10/2 cable though.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #20

    Aug 20, 2008, 11:45 AM
    Stan,

    My original error was caused by a loose nut on my keyboard. :)

    This morning when I re-started the conductor size calculator instead of toggling the radio button for "Continuous Load", I placed 26 Amps into the Continuous Load block and out popped the size #8 AWG and a 40 Amp breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire service, wire gauge 100 amp [ 9 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...

Wire Gauge? [ 7 Answers ]

I've been looking for 2 days for an online wire gauge calculator. I'm going to relocate my meter to the side of my house (converting from overhead to underground service), then I'm going to remove the existing electrical panel (from the outside of the house) and install a breaker panel on the...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...

Gauge of wire? [ 1 Answers ]

Thank you for responding. I would like to know what size of wire I need to run a circuit 125 amp, 240V to a sub panel 244 feet away? Or, what size of wire I need to run a circuit 60 amp, 240V to a sub panel 244 feew away? Thank you in advance

Proper gauge wire to run to hot tub? [ 5 Answers ]

I am trying to run wiring from my main service panel to a hot tub on our back porch. My father was an electrician, so I have a fairly good base of knowledge, but I wish he was alive to help me out. To save on the electrician install, I was going to install the 240 breaker in the box and then run...


View more questions Search