    4 wire 100amp service box but only 3 wires?
    :confused: 4 wire 100amp service box but only 3 wires?
    I replaced my water heater with a tankless water heater. My service box is set up for hot, hot, neutral, and appliance ground for 220 watt hook up. But the water heater only has 3 wires, hot hot, and "Bare wire" ground. I currently have the water heater connected as, hot, hot, to breaker, and the bare ground wire to appliance ground. Is this correct? As I have been experiencing ground fault type shocks through out the house ever since I installed the water heater. How can I correct this and eliminate the shocks from touching other appliances in the house. Breaker box is in the house,(Trailer), has separate ground wire to the ground, then Hot, Hot, and Neutral to outside pole w/ 100 amp service disconnect box w/ 100amp fuses.
    Credendovidis's Avatar
    Credendovidis Posts: 1,593, Reputation: 66
    -
     
    #2

    Apr 2, 2008, 02:39 AM
    Quote Originally Posted by ishare
    :confused:
    You have a two-phase 220 Volt supply (hot-hot), a neutral for 110 Volt supply with any of the hot wires, and a ground.
    .
    General :
    .
    Any 220 Volt appliance requires 2 hot's and a ground. A neutral wire is in this specific circuit not needed. The "bare" wire is a ground wire.
    .
    Any 110 Volt appliance requires one hot, one neutral, and one ground wire.
    .
    Water heater
    .
    If the water heater is a 220 Volt type, the neutral wire remains unconnected.
    The shocks you experience indicate that you most probably have connected the ground to the neutral wire, or one of them to some hot point, or (instead of the ground wire) the neutral to the heater ground. Just check your wiring.
    .
    Alternatively there also may be an isolation leak in the heater to ground.
    To check disconnect the hot wires of the heater and check if the shock problem is still there. If so, the problem is elsewhere. If the problem is gone, use a multimeter to check the isolation between the earth points and either hot wire. Note that there is only an electric connection between heating element and wiring if there is water pressure and the tap is open. A pressure sensor inside the heater only makes an electric connection under these conditions. So either open up the heater unit to measure between the actual heater wires and ground, or apply tap water and open the warm water tap and measure between the normal connections.
    .
    Ground
    .
    The data you provided allows for even one more possible ADDITIONAL cause for your shock problem : your ground wire may be connected to a very poor ground point. A good ground will prevent you from feeling any shocks on appliances. Have your ground point checked by a professional. It may be so poor, that leak currents are not grounded properly.
    A good ground could save your life.
    .
    Success!
    As always : if you require more info, please let me know. If this solves your problem, please rate the answer provided! Feed back is always appreciated!
    ;)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Apr 2, 2008, 03:56 AM
    Quote Originally Posted by ishare
    Breaker box is in the house,(Trailer), has separate ground wire to the ground, then Hot, Hot, and Neutral to outside pole w/ 100 amp service disconnect box w/ 100amp fuses.
    Exaplain this a little better.
    Do you actually have only three wires going out to the pole from the trailer? What is this ground you are talking about? Where does it go and where is it connected on both ends?

    What about the ground from the water heater? Where is that connected in the panel? There should be two separate bars for grounds and neutrals in your panel.

    A mobile homes requires FOUR wires back to the service equipment. A grounding conductor is mandatory, this is where you get your safety ground that prevents the problems you are describing.
    I suspect this ground is no correct and giving your these issues.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

4 wire 100amp service box but only 3 wires? [ 1 Answers ]

I replaced my water heater with a tankless water heater. My service box is set up for hot, hot, neutral, and appliance ground for 220 watt hook up. But the water heater only has 3 wires, hot hot, and "Bare wire" ground. I currently have the water heater connected as, hot, hot, to breaker, and the...

Upgrading from 100amp service to 200 amp service [ 1 Answers ]

I have a 1994 model double wide home, and would like to change my 100 amp service to 200 amp service. ( I want to go to electric heat) I have a disconnect at the house after the meter and it say 200amp. Is the wiring from there to my breaker box able to handle 200 amp service, and if not how do I...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...

100Amp disconnect panel before 100Amp main pannel [ 5 Answers ]

I would like to relocate my main 100Amp panel to the inside wall of my garage. Code saids the main panel must be on an outside wall. What I was thinking of doing Is install a New Main panel on the inside wall of the garage and put a 100Amp disconnect at the old panel location. I am aware of...

Hard wire 3 wire to 4 wire 220 service [ 2 Answers ]

How do I hard wire my 3 wire (red,blk & bare copper wires) 220vac cooktop to the 4 wire (black/white stripe,black/red stripe, blk/blk & bare alum wires) in the house supply j-box ?


View more questions Search