Dec 14, 2008, 10:43 AM
|
|
Neutral/Ground bus bar?
I am installing a sub panel in my basement to run some extra circuits for a bathroom, spare room etc.
I am putting a 60 amp fuse in the main service panel, running a 6-3 wire with ground and back feeding the new sub panel.
The new panel does not come with a ground bus bar, and suggests using the neutral bus bar for ground. This doesn't seem right to me, it also suggests putting a ground bus bar (not provided with the box) when necessary.
So, should I install a new bus bar for the ground? Use the neutral for ground?
|
|
|
Electrical & Lighting Expert
|
|
Dec 14, 2008, 11:48 AM
|
|
There is a bond screw/strap included with your new panel. DO NOT install it.
You must get a separate add-on ground bar for this sub-panel which screws right to the back of the panel. Only grounds must go on it.
The neutrals must stay on the neutral bar
|
|
|
New Member
|
|
Dec 14, 2008, 11:59 AM
|
|
That is what I thought, but why would they suggest using the neutral bus bar for the ground wire?
Thanks for your response.
|
|
|
Electrical & Lighting Expert
|
|
Dec 14, 2008, 12:02 PM
|
|
Originally Posted by Laurenceio
That is what i thought, but why would they suggest using the neutral bus bar for the ground wire?
If this panel were to used as service equipment (main panel) the neutral bar would be bonded to the panel box and the same bar be used for both grounds and neutrals
|
|
|
New Member
|
|
Dec 14, 2008, 12:16 PM
|
|
I see (at least I think so). In short, I need to install a ground bus bar don't I. The Ground wire from the new wire (6-3 with ground) goes into this new bus bar and provides my ground then.
However, does this mean that on my main panel ( I will go look when I get a chance too later) the ground and neutral share the same bus?
|
|
|
Electrical & Lighting Expert
|
|
Dec 14, 2008, 12:24 PM
|
|
Originally Posted by Laurenceio
I see (at least I think so). In short, I need to install a ground bus bar don't I. The Ground wire from the new wire (6-3 with ground) goes into this new bus bar and provides my ground then.
However, does this mean that on my main panel ( I will go look when I get a chance too later) the ground and neutral share the same bus?
Exactly. :cool:
|
|
|
New Member
|
|
Dec 14, 2008, 12:58 PM
|
|
Stanfortyman, Thanks for your help.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Neutral / Ground
[ 3 Answers ]
OK Strat,
Here is the photo clip of the schematic of the Neutral /Grounding system in my place.
Don
Ground bar vs. Neutral bar
[ 1 Answers ]
What is the difference? I understand the neutral goes on the neutral bar and the same for the ground wires but if you were to check continuity between the neutral bar and ground bar they are connected. Can you explain?
Open ground when neutral not touching ground
[ 3 Answers ]
Hi,
I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to.
It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...
Ground and neutral bar
[ 2 Answers ]
I'm installing a 4 wire, 50 AMP GFCI for my hot tub. My question is at my main breaker for the house where I'm taking power from, which bar is neutral and which bar is ground, or does it matter?
Thanks
Fred
Using Neutral as a Ground ?
[ 3 Answers ]
In my new apartment there are some wall outlets that are two prong outlets. Also my fear is that the three prong outlets are not “physically” connected to ground. I heard somewhere that in this kind of system the neutral wire can also be used as a ground. Is this correct? Would a separate...
View more questions
Search
|