    Will a 208 volt 3 phase mixer work off a 240 volt 3 phase service?
    I have 240 volt 3 phase service and I have a 208 volt 3 phase mixer. Can I hook it up to the 240 volt 3 phase service? Also I have a 208 volt 3 phase oven will it work for that as well?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Jan 23, 2009, 06:17 PM
    No name plate on the mixer? Call the Mfg. and ask. My guess would be yes... but you need to verify with the mfg. 'Most" equipment will work with a -15% / +15% voltage variance. But verify first.
    andrewc24301's Avatar
    andrewc24301 Posts: 374, Reputation: 29
    Full Member
     
    #3

    Jan 23, 2009, 06:50 PM

    If you give me the model serial, and who made it, I can look and see.

    Same goes for the oven.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Jan 23, 2009, 07:04 PM

    I would say yes. 110vs120, compatible

    220vs240, compatible.

    208 would fall into the category of 220/240.

    The most important part is that it is three phase. The next step up would be 480 three phase. I believe that 208 three phase would be just fine on a 240 three phase, I think its basically the same thing. (electricians, please correct me if I'm wrong).
    andrewc24301's Avatar
    andrewc24301 Posts: 374, Reputation: 29
    Full Member
     
    #5

    Jan 23, 2009, 07:18 PM
    Quote Originally Posted by mygirlsdad77 View Post
    i would say yes. 110vs120,, compatible

    220vs240, compatible.

    208 would fall into the catagory of 220/240.

    The most important part is that it is three phase. The next step up would be 480 three phase. I believe that 208 three phase would be just fine on a 240 three phase, i think its basically the same thing. (electricians, please correct me if im wrong).

    True 90% of the time. But there are instances where it does make a difference.

    The data plate might even answer his question, it may say something to to tune of "VOLTAGE 200-250" or something of that nature.

    Older mixers would probably be all right, but newer machines can be real finicky.

    If I can't find it in the book, I can find out Monday for sure.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Jan 23, 2009, 07:24 PM

    Okay, looking forward to info.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jan 23, 2009, 08:09 PM
    I won't kill a motor too quickly, but 208v 3-phase is NOT the same thing as 240v 3-phase.

    Don't forget, 240v 3-phase has a high leg. If this is a 5-wire circuit (having a neutral) you'd better be sure the 120v loads are not on the high leg.
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #8

    Jan 23, 2009, 08:17 PM

    We install 208 and 240 equipment all the time ( Ok, I sell and don't do the actual install)

    We come across machines all the time, I see at least one a week, where a motor has gone out early from not being the right voltage.

    They normally will just go out early, shorten the life of the motor

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

208 Volt Single phase vs 230 Volt single phase [ 3 Answers ]

I have a commercial appliance that is rated for 230 volt single phase. All I have available is 208 volt single phase. Will the unit work on 208V or do I have a problem?

208 volt3 phase why to single phase 120 volt [ 4 Answers ]

Supply is from 75 kva transformer, 3 phase delta /y three wire feeding a 30 amp breaker. 100 feet down stream is a junction box that I want to tap and produce a 120 v single phase ( 20 amp CB) supply. The junction box feeds a 6 amp motor

3 phase 230 volt panel [ 4 Answers ]

I have a 3 phase 230 volt 3 wire panel that has a 120, 120 & 208 volts phase to ground and 230, 230, & 230 phase to phase.The AC guy came and installed a new 208/230 volt 3 phase unit. He measured above voltages and told me since one of the voltages is 208 we have to fix that problem first. Do you...

How am I going to size my 3 phase X'mer with 1 phase load using current as reference [ 3 Answers ]

Hi, I'm Peping: I have 90 pieces of single phase loads with current of 2 Amperes. This will be loaded to a 3 phase transformer, Wye connected having a line to line voltage of 220 Volts. What will be the size of the transformer required for the mentioned loads? Many thanks, Peping

3 phase 208 volt/120 volt .load [ 1 Answers ]

I am trying to hook up a commercial espresso machine which has a 220 line. My existing electrical box is a 3 phase 208 volt/120 volt. Would this be sufficient to handle this?? Thank you


View more questions Search