    200 amp. Main panel, fed from the meter. How do a I Install a 200 amp sub-panel
    I have a 200 amp panel, fed from the meter located in the house. I want to add another 200 amp.sub-panel in the garage, how can I connect the two? And if so what size of wire do I use?
    Thank's
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jun 23, 2013, 06:54 PM
    It is almost certain that the largest feeder that you can pull from that 200A panel is 125A. Check the label inside the door.
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #3

    Jun 25, 2013, 08:19 PM
    Why would you want a 200 amp subpanel in your garage?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jun 26, 2013, 03:42 AM
    This is 562349's second thread on this project and he has not replied to either one.
    Let's see if he breaks tradition and does the polite thing and replies to at least one of them.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Main 200 amp. Installing a 200 amp sub-panel. Wire size jumper to connect(2 /100 amp) [ 1 Answers ]

Installing a 200 amp.sub-pane (type D- Hom), the main panel is 200 amp.also, I'm using 2 /100 amp. Breakers. My question is : what wire size do I need for the jumper to connect the two breakers. I'm using #2 X3 and #4 ground wire to connect the sub-panel, do I need the same#2 for the jumper? Or...

How to install a 100 amp sub panel with a 200 amp main [ 4 Answers ]

I am installing a 100 amp sub panel beside a 200 amp main in my basement due to refinishing my basement and my main is full. My question is, is there a certain spot in the main that the 100 amp breaker needs to be installed that will power the sub panel?

Can I install a 150 amp sub panel to a 200 amp panel with the sub running (3) 50 amp [ 13 Answers ]

I have square D QO panel. I am adding a Stiebel 29 on demand water heater and it calls for (3) 50 amp 240V breakers. Can I add a subpanel that has (3) 50 amp breakers to tie into my existing 200 amp service? If so what gauge copper wire would connect the two and does Square D QO make a 150 amp...

Main Cutoffs: 200 amp outside panel feeding a 200 amp inside circuit breaker panel. [ 1 Answers ]

Would you please clarify an answer you gave to a previous question? Your answer makes me wonder about the capacity of the main shut-off circuit breaker in an inside circuit breaker panel. Is the inside circuit breaker panel the same as what you call a subpanel? Here's the question and answer:...