    Breaker box
    My main beaker in my box is 200 can I go over that
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 11, 2012, 02:29 AM
    Sure providing you have a larger service entrance conduit, wire ,meter etc.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #3

    Oct 13, 2012, 01:45 PM
    Sure, airplanes do all the time
    jefferson17's Avatar
    jefferson17 Posts: 17, Reputation: 2
    New Member
     
    #4

    Oct 18, 2012, 10:38 PM
    Sure but the service wire coming into your house from the street is probably only rated for 200 amps. So you'd need to replace your service with something bigger than 200.

    Or... add a new service and panel. Do you REALLY need more than 200 amps? What's going on?
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #5

    Oct 19, 2012, 05:04 AM
    What do you mean? If you mean can the sum of all the breakers in the panel exceed 200 amps? Then yes. You can have say, 300 amps worth of breakers because it's unlikely you will have a full load on all circuits at the same time.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 19, 2012, 11:34 AM
    Adding the sum of the ratings of circuit breakers in any panel is meaningless and irrelevant.

    Performing the appropriate load calculation listed in Article 220 of the NEC is the only method of calculating a service size.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #7

    Oct 19, 2012, 11:37 AM
    I agree, but I think that is what the OP is doing. He needs to do a load calc.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between twin breaker and quad breaker siemens [ 2 Answers ]

What is th difference between a duplex 20/20 breaker and a 20/20 twin breaker siemens brand

Issues when replacing single circuit breaker with duplex breaker [ 3 Answers ]

I have a Westinghouse B20 2040CT Circuit Breaker Panel with a 200 amp main. I am remodeling my kitchen and would like to correct some of the current wiring problems I inherited when I purchased the house. A number of circuits are current heavily loaded and I want to take this opportunity to...

Can I tapinto the line side of a100 amp main breaker to feed a 60 amp breaker service [ 1 Answers ]

Can I tap into the line side of a 100 amp main breaker to feed a 60 amp breaker for a electric stove


View more questions Search