    Thermostat which operates a 1-amp fan?
    A fan pulls air into the house beneath the structural wood floor to keep the space dry.
    Can a thermostat operate this fan directly from the thermostat's contacts, or must I place another switching circuit, operated by the thermostat, which switches the power to the fan on and off?

    Thank you,

    Robert
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 18, 2010, 04:13 AM
    A line voltage thermostat is usually rated 22 amps, so you can use one stat to operate this fan directly.

    How do you plan to use a thermostat? Do you want fan on when temperature rises or falls?

    I would think that a humidistat would work better, as moisture rises, stat would close and turn fan on.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    May 18, 2010, 05:34 AM

    If you mean a 24 Volt thermostat, you may need a contactor, not sure their capacity for current.
    Robert Gift's Avatar
    Robert Gift Posts: 100, Reputation: 3
    Junior Member
     
    #4

    May 18, 2010, 07:53 AM

    Thank you.

    I want to warm our cold basement by pulling the cold air out which would pull warmer air inside.

    120 Volt fan.
    It is the amperage of a contact which matters more than voltage.

    We happen to have a thermostat with mercury globule in glass tube which bridges two conductors. What kind of amperage that would allow?

    Is that the same way a 15-amp mercury "silent" switch works?
    I never see such switches any more. Banned due to mercury contamination if a fire?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    May 18, 2010, 08:03 AM

    Voltage, current, AC/DC, HP ALL matter.

    Voltage: Contacts can arc
    DC vs AC: Arc supression is done in some AC contactors
    Current: Contacts get hot and melt
    HP: Is a different animal where starting current can be larger than running current hence the peak current the switch can handle is more.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    May 18, 2010, 09:06 AM
    First you stated you wanted to remove moisture, now you want to heat the space.

    Please provide ALL detail when asking a question.

    Drawing warm air into a cold space can create more condensation to accumulate, and defeat the purpose of what your trying to do, whatever that is. So think about what your trying to accomplish.

    This statement you made is incorrect:

    It is the amperage of a contact which matters more than voltage.

    Anything that handles electricity will be rated to handle a certain amount of amps and voltage.


    The stat you have with a mercury bubble sounds like a low voltage unit, and not be able to handle 120 volts. You need to confirm the voltage rating of any stat you plan to use.

    Second, stats using mercury are not allowed to be used any longer.

    So, what do you really want to get done here?
    Robert Gift's Avatar
    Robert Gift Posts: 100, Reputation: 3
    Junior Member
     
    #7

    May 18, 2010, 10:56 AM

    I want to do both.
    Pull warm dry air into the space between the structural wood floor and barearth, and use another fan to pull cold air out of the basement which is replaced with warm dry air from outside.

    Wish I could find a mercury light switch to see if there is a difference between the hermetically sealed ampules. This one mercury thermostat has a lot of mercury in two glass vials. Maybe it has four vials.

    Thank you.
    ceilingfanrepair's Avatar
    ceilingfanrepair Posts: 5,733, Reputation: 109
    Uber Member
     
    #8

    May 18, 2010, 12:31 PM

    They make gable fans with built in thermostats. I use one to cool an attic storage space. Works great, around $50 at Home Depot.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #9

    May 18, 2010, 12:34 PM
    Yea CFR, but those would be close on temp rise stat, and Robert, if I am reading him correctly, will need a open on temp rise stat.
    Robert Gift's Avatar
    Robert Gift Posts: 100, Reputation: 3
    Junior Member
     
    #10

    May 18, 2010, 02:48 PM

    Thanks, CFR and TK.

    Best to have fans ON when outside temperatureaches 70F.
    The warm dry air is pulled into the basement both above and below the floor.

    With thermostats I could experiment with what is most efficient.
    Often I am too cold when in the unfinished basement but air outside is warm and dry.
    A "humistat"(?) turns on the underfloor fan if the humidity gets high enough. But I have never seen the fan operate. When set to low humidity, the fan does turn on.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #11

    May 19, 2010, 05:34 PM
    There are line voltage thermostats that can handle the switching for you. Specifically made for greenhouse cooling operations, then will turn on the load as temperature rises. You may want to consider a humidistat as well to prevent humid air from being introduced.
    Robert Gift's Avatar
    Robert Gift Posts: 100, Reputation: 3
    Junior Member
     
    #12

    May 20, 2010, 12:49 PM
    Quote Originally Posted by Missouri Bound View Post
    There are line voltage thermostats that can handle the switching for you. Specifically made for greenhouse cooling operations, then will turn on the load as temperature rises. You may want to consider a humidistat as well to prevent humid air from being introduced.
    Thanks MB.
    I'll go look.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a Cassablanca fan and light to a wall switch that operates each function seper [ 4 Answers ]

I am trying to connect a ceiling fan and light kit to an exsisting wall switch. My problem is there 4 wires to the fan switch and only two wires from the wall. Can you help me?

Ceiling fan doesn't operates by pull chain only, not wall switch. [ 9 Answers ]

If a ceiling light is controlled by a wall switch, along with one wall outlet on the same wall as the switch, what would cause the switch to become inactive after a hampton bay ceiling fan is installed in place of the ceiling light? The ceiling box has only black, white and ground wire, and the...

NEW Harbor Breeze fan only operates in high speed [ 1 Answers ]

Hello, I recently installed a new Harbor Breeze ceiling fan with light kit, remote and no pull chains. I have installed numerous ceiling fans before without any previous problems. This fan in question operated A-OK for the first day or two. Now, the fan only operates in high speed, no matter...

Transmitter operates fan in other room too [ 1 Answers ]

I just had a Veranda ceiling fan installed. This fan is in second floor bedroom. I have a fan in kitchen on first floor, opposite side of house. It has the same type of wall transmitter. Either wall transmitter operates both fans. If I turn on fan and/or light in bedroom, it will turn it on in...

Installing Thermostat Ceiling Fan & Light Remote Control [ 1 Answers ]

I am installing a HarborBreeze Thermostate Ceiling Fan & Light Remote Control on a standard ceiling fan (no I can't find the brand or model name) with a pull chain for the light and a pull chain for the speeds. There are 3 speeds on the fan. My problem is that there are only five wires on the...


View more questions Search