Will a 208 volt 3 phase mixer work off a 240 volt 3 phase service?
I have 240 volt 3 phase service and I have a 208 volt 3 phase mixer. Can I hook it up to the 240 volt 3 phase service? Also I have a 208 volt 3 phase oven will it work for that as well?
|
|
|
Ultra Member
|
|
Jan 23, 2009, 06:17 PM
|
|
No name plate on the mixer? Call the Mfg. and ask. My guess would be yes... but you need to verify with the mfg. 'Most" equipment will work with a -15% / +15% voltage variance. But verify first.
|
|
|
Full Member
|
|
Jan 23, 2009, 06:50 PM
|
|
If you give me the model serial, and who made it, I can look and see.
Same goes for the oven.
|
|
|
Plumbing Expert
|
|
Jan 23, 2009, 07:04 PM
|
|
I would say yes. 110vs120, compatible
220vs240, compatible.
208 would fall into the category of 220/240.
The most important part is that it is three phase. The next step up would be 480 three phase. I believe that 208 three phase would be just fine on a 240 three phase, I think its basically the same thing. (electricians, please correct me if I'm wrong).
|
|
|
Full Member
|
|
Jan 23, 2009, 07:18 PM
|
|
Originally Posted by mygirlsdad77
i would say yes. 110vs120,, compatible
220vs240, compatible.
208 would fall into the catagory of 220/240.
The most important part is that it is three phase. The next step up would be 480 three phase. I believe that 208 three phase would be just fine on a 240 three phase, i think its basically the same thing. (electricians, please correct me if im wrong).
True 90% of the time. But there are instances where it does make a difference.
The data plate might even answer his question, it may say something to to tune of "VOLTAGE 200-250" or something of that nature.
Older mixers would probably be all right, but newer machines can be real finicky.
If I can't find it in the book, I can find out Monday for sure.
|
|
|
Plumbing Expert
|
|
Jan 23, 2009, 07:24 PM
|
|
Okay, looking forward to info.
|
|
|
Electrical & Lighting Expert
|
|
Jan 23, 2009, 08:09 PM
|
|
I won't kill a motor too quickly, but 208v 3-phase is NOT the same thing as 240v 3-phase.
Don't forget, 240v 3-phase has a high leg. If this is a 5-wire circuit (having a neutral) you'd better be sure the 120v loads are not on the high leg.
|
|
|
Expert
|
|
Jan 23, 2009, 08:17 PM
|
|
We install 208 and 240 equipment all the time ( Ok, I sell and don't do the actual install)
We come across machines all the time, I see at least one a week, where a motor has gone out early from not being the right voltage.
They normally will just go out early, shorten the life of the motor
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
208 volt3 phase why to single phase 120 volt
[ 4 Answers ]
Supply is from 75 kva transformer, 3 phase delta /y three wire feeding a 30 amp breaker. 100 feet down stream is a junction box that I want to tap and produce a 120 v single phase ( 20 amp CB) supply. The junction box feeds a 6 amp motor
3 phase 230 volt panel
[ 4 Answers ]
I have a 3 phase 230 volt 3 wire panel that has a 120, 120 & 208 volts phase to ground and 230, 230, & 230 phase to phase.The AC guy came and installed a new 208/230 volt 3 phase unit. He measured above voltages and told me since one of the voltages is 208 we have to fix that problem first. Do you...
3 phase 208 volt/120 volt .load
[ 1 Answers ]