    I am remodeling my kitchen. It currently has 1 50A breaker for the electric range. I want to install a 36" cooktop and 30" wall oven. Can I install both of these on the existing 50A 240v breaker?

    I checked ratings for some of the models that I am considering, and combined they average about 13.5kw to 14.5kw.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #2

    Sep 12, 2008, 01:02 AM
    Yes, you can. If you stay under 15kw

    The NEC allows you to add the ratings of one cooktop and up to two wall mounted ovens and treat it as a single range provided they are all on the same circuit and in the same room. Using Table 220.55 of the NEC the circuit for a 15kw range would need to be rated for 8kw with 5% added for each kw over 12 that your setup actually is.

    About 9.26kw in this case. 9260w divided by 240v equals about 39 amps. Take into account the circuit needing to be sized at 125% since this is considered a continuous load and you come up with 48.75 amps. The next breaker size up is 50A which is what you have.
    bergie33's Avatar
    bergie33 Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 12, 2008, 05:07 AM
    This is definitely the answer I was hoping to get. Thank you.


    Quote Originally Posted by Tev
    Yes, you can. If you stay under 15kw

    The NEC allows you to add the ratings of one cooktop and up to two wall mounted ovens and treat it as a single range provided they are all on the same circuit and in the same room. Using Table 220.55 of the NEC the circuit for a 15kw range would need to be rated for 8kw with 5% added for each kw over 12 that your setup actually is.

    About 9.26kw in this case. 9260w divided by 240v equals about 39 amps. Take into account the circuit needing to be sized at 125% since this is considered a continuous load and you come up with 48.75 amps. The next breaker size up is 50A which is what you have.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installation of a gas cooktop over a gas oven [ 1 Answers ]

I want to install a gas cooktop over a built-in gas oven in a under the counter cabinet.. I understand that this configuration is not normally done.. (installation is normally a gas cooktop with an electric built-in oven combination)... Is there a code specification that I must follow for this...

Does in-the-floor heating really need a separate circuit? [ 8 Answers ]

I want to put in under-the-tile floor heating in my bathroom, which is being renovated. The instructions that come with the heating cable say that the circuit for the heating wire must be separate. This is impossible to do! The heating wire that would go in is rated at only 300 watts. Is there...

Single 40 amp circuit, cooktop requires 40amps and Oven 30amps [ 4 Answers ]

I am replacing an electric cooktop and oven. The original cooktop and oven were connected to one 40 amp circuit. The replacement cooktop is calling for a 40 amp circuit and the oven is calling for 30 amps. Can I install both on a the 40 amp circuit?

Wall oven [ 2 Answers ]

I got new wall oven. It was working for a while now it's not working. Oven light, clock and all buttons are working but the when I set it for bake it does not warm up. I have it connected directly to 220 volt outlet. Do I need fuse panel between oven and power outlet?

220v oven circuit [ 1 Answers ]

I've built a powder coating oven using 2 oven heating elements... Question: I have a 4 wire 220v A/C circuit installed by an electrician. Color codes are B/W/R/G. I understand the green is the ground, White is neutral,Blk is 110v and red is 110v. The controller (switch) is 3 terminal in a...


View more questions Search