#1  
Old Mar 31, 2008, 11:59 AM
Z280Bill
New Member
Z280Bill is offline
 
Join Date: Mar 2008
Posts: 3
Z280Bill See this member's comment history on his/her Profile page.
Upgrading to 200 amp service

I want to upgrade from 150 to 200 Amp service. My current panel has double breakers in ever slot except where the A/C, Dryer and Range are connected. I have wired panels before but never upgraded the service. I have studied and planned the change over the last two months but I still have a question on the grounding. Currently my panel is a main breaker panel and it is grounded to the water pipe (No Grounding electrodes). My service comes in approximately 70 feet from where my panel is located. I am replacing the meter box with one that has the meter on one side and the 200 main on the other. I am running 4 awg 4/0 cable from the new meter/switch panel to the new breaker panel. My county requires NEC2005 codes, where and how do I ground this system to code? Does all of the grounding take place from the new meter/switch panel or am I required to also ground the main lug panel? Does it matter which hot runs to which bus bar? or whether I locate the neutrals on the left and the grounds on the right?

Reply With Quote
 
     

Answers
 
 
Old Mar 31, 2008, 01:00 PM   #2  
stanfortyman
Electrical & Lighting Expert
stanfortyman is offline
 
Join Date: Feb 2008
Posts: 831
stanfortyman See this member's comment history on his/her Profile page.
Your grounding electrode conductors AND water bond/electrode conductors all go to the main disconnect.
You will need a #4cu to the water pipe and connect within 5' of where the pipe enters. You must also jump around any meters or plastic fittings such as filters.
You also need at least one ground rod to supplement the water pipe electrode. The wire to this can be a #6cu and should go from the disconnect right to the ground rod(s). Some areas accept one ground rod, some require the 25 ohm test and will simply require a second rod installed. You are NOT required to install any more than two rods.

You DO NOT have to run four 4/0AL wires to the panel. You can reduce the neutral to a 2/0AL and ground does not need to be any bigger than #6cu or #4al.
You can use anything larger if you desire, but the sizes mentioned are code.
There's NO way I'd personally run FOUR 4/0al if I didn't have to.

Comments on this post
Z280Bill agrees: Sounds accurate and is well appreciated, Thanks
  Reply With Quote
 
     


Question Tools Search this Question
Search this Question:

Advanced Search
Display Modes

 
Similar Sponsors

Similar Questions
Question Asker Topic Answers Last Post
upgrading from 100amp service to 200 amp service Gerald1972 Electrical & Lighting 1 Jan 16, 2008 09:58 AM
400 amp service with 2-200 amp panels & 320 amp socket jimmyj71 Electrical & Lighting 6 Oct 31, 2007 09:20 AM
upgrading to 200 amp with connection issues alohabob Electrical & Lighting 11 Mar 17, 2007 12:44 PM
runing 100 amp sevice panal 200 ft away from main 200 amp service jpriest6523 Electrical & Lighting 1 Feb 5, 2007 12:49 AM
200 amp service with a 200 amp outdoor breaker robertmerritt2 Electrical & Lighting 1 Aug 25, 2006 12:40 PM




Copyright ©2003 - 2007, Ask Me Help Desk.
All times are GMT -8. The time now is 11:48 AM.

Content Relevant URLs by vBSEO 3.0.0 RC6 © 2006, Crawlability, Inc.