Thread Tools Display Modes
Question
 
 
#1  
Old Jul 16, 2008, 03:49 PM
catrains
New Member
catrains is offline
 
Join Date: Jul 2008
Posts: 5
catrains See this member's comment history on his/her Profile page.
How do I wire the hot water heater to breaker

My husband is out of town and the electric hot water heater stopped functioning...the breaker at the main breaker box was tripping...i replaced the breaker at the main box...it still tripped...the hot water heater also has a breaker that connects to the main breaker box...i had to replace the entire breaker box because the old one was old...i replaced it with what it had before, a 30 amp 2-pole breaker...now i don't think i have it wired right...it is still tripping...i did my best to copy it from the other one, but this one has extra screws...i am not completely without knowledge, but i do need the simplified version...i am attaching an image...keep in mind that i do not know what is the ground...or the hot wires...if you will tell me what color wire goes where, i will be good...thanks..i hope you can help...been without hot water for some time now...

Attached Files
File Type: zip breaker box.zip (27.2 KB, 19 views)
Reply With Quote
 
     

Answers
 
 
Old Jul 16, 2008, 04:26 PM   #2  
Junior Member
Missouri Bound is offline
 
Join Date: Dec 2005
Posts: 199
Missouri Bound See this member's comment history on his/her Profile page.
If you duplicated the wiring from the old to new, you probably did it correctly.
As for the breaker tripping, it's probably an issue with the water heater. Most water heaters fail with open elements, and some fail with the controls and allow both elements to come on at once....which is too high of a load for the breaker. Have the water heater checked.
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 04:34 PM   #3  
Printers & Electronics Expert
donf is offline
 
donf's Avatar
 
Join Date: Aug 2007
Location: Tidewater, Virginia
Posts: 1,986
donf See this member's comment history on his/her Profile page.donf See this member's comment history on his/her Profile page.
Cat,

Usually, you do not use two double breakers.

You normally would find one 240 VAC breaker in the main panel to feed the water heater, unless you are using a sub panel. However, if you replaced both breakers, then the problem may be the water heater itself.

Electrically speaking, you need two hots (these would be the Black and the Red conductors) Each of these conductors connect to one of the terminals on the 30 amp breaker. The White is the Neutral conductor and the bare wire or green wire is the ground.

The voltage across the Black to Red conductors will be 240 VAC. The voltage between Black and White will be 120 VAC and the voltage between the Red and White will also be 120 VAC.

I do not understand why there would be a second breaker in the branch circuit from the main panel, but I cannot see what you are seeing.

My suggestions are:
1) Call and electrician or a plumber because what has to be determined is whether you have an electrical failure or a short within the water heater itself. If you are wired correctly, your breaker should not trip. You can test this by disconnecting the water heater from the circuit and seeing if the breaker trips. If it does, then you have an electrical problem external to the water heater.

2) If the breaker trips as soon as you turn the power on to the water heater (with the heater connected) then you may well have a short on the heater.

The voltage and the amperage that the water heater uses is well within the killing range, so please do not try to be a hero and get someone to help you!
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 05:03 PM   #4  
Electrical & Lighting Expert
Washington1 is offline
 
Join Date: Jun 2007
Posts: 680
Washington1 See this member's comment history on his/her Profile page.
Quote:
Originally Posted by catrains
My husband is out of town and the electric hot water heater stopped functioning...the breaker at the main breaker box was tripping...i replaced the breaker at the main box...it still tripped...the hot water heater also has a breaker that connects to the main breaker box...i had to replace the entire breaker box because the old one was old...i replaced it with what it had before, a 30 amp 2-pole breaker...now i don't think i have it wired right...it is still tripping...i did my best to copy it from the other one, but this one has extra screws...i am not completely without knowledge, but i do need the simplified version...i am attaching an image...keep in mind that i do not know what is the ground...or the hot wires...if you will tell me what color wire goes where, i will be good...thanks..i hope you can help...been without hot water for some time now...

Can you send the manfactures name and model number. I've never seen an H20 (accept some tankless water heaters)with a neutral.

The disconnect may have been installed based on the within sight rule, or just because.

Please send your information.

PS: Do not keep trying to re-set the breaker until we figure this out.
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 05:13 PM   #5  
Electrical & Lighting Expert
Washington1 is offline
 
Join Date: Jun 2007
Posts: 680
Washington1 See this member's comment history on his/her Profile page.
Cat,

I hope you didn't fire-up (AKA:Power-up) the water heater without water in it??

Comments on this post
JustMarried614 agrees: yeah no kidding!
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 05:56 PM   #6  
New Member
catrains is offline
 
Join Date: Jul 2008
Posts: 5
catrains See this member's comment history on his/her Profile page.
Quote:
Originally Posted by donf
Cat,

Usually, you do not use two double breakers.

You normally would find one 240 VAC breaker in the main panel to feed the water heater, unless you are using a sub panel. However, if you replaced both breakers, then the problem may be the water heater itself.

Electrically speaking, you need two hots (these would be the Black and the Red conductors) Each of these conductors connect to one of the terminals on the 30 amp breaker. The White is the Neutral conductor and the bare wire or green wire is the ground.

The voltage across the Black to Red conductors will be 240 VAC. The voltage between Black and White will be 120 VAC and the voltage between the Red and White will also be 120 VAC.

I do not understand why there would be a second breaker in the branch circuit from the main panel, but I cannot see what you are seeing.

My suggestions are:
1) Call and electrician or a plumber because what has to be determined is whether you have an electrical failure or a short within the water heater itself. If you are wired correctly, your breaker should not trip. You can test this by disconnecting the water heater from the circuit and seeing if the breaker trips. If it does, then you have an electrical problem external to the water heater.

2) If the breaker trips as soon as you turn the power on to the water heater (with the heater connected) then you may well have a short on the heater.

The voltage and the amperage that the water heater uses is well within the killing range, so please do not try to be a hero and get someone to help you!


Don,
The break located near the water heater that comes off of the main breaker box has 2- 30 amp breakers...that is what was there before...Not to be a smart , but if i could afford the rate of an electrician I would have done that...I will test the water heater by doing what you said though...i would not even think of being a hero...i have tons of respect for electricity...the hot water heater definately has water in it...my husband replaced one of the heating elements a few months back and it worked for a while after that...it has two heating elements...one on top and one on bottom...my understanding is that the one on the bottom is not being used...he replaced the one on top...i will check the water heater for a short...my husband works in a/c and heating...i have a meter. i have done some reading up on all of this and found out that i have 2 hot and one neutral coming from the main breaker and the same coming from the water heater...
could it be a fuse to the breaker...i don't know if this has one, but i can look if you can give me an idea of where it might be...thanks for the info...if you have any more advice, please don't hold back...
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 06:04 PM   #7  
New Member
catrains is offline
 
Join Date: Jul 2008
Posts: 5
catrains See this member's comment history on his/her Profile page.
Quote:
Originally Posted by Washington1
Can you send the manfactures name and model number. I've never seen an H20 (accept some tankless water heaters)with a neutral.

The disconnect may have been installed based on the within sight rule, or just because.

Please send your information.

PS: Do not keep trying to re-set the breaker until we figure this out.


the model number is 64020RS...the manufacturer is Reliance...the tank is full of water...will not reset breaker...i think i will start looking at the water heater now...i have replaced both breakers and still tripping...checking the water heater is easier than tracing the wiring i think...i don't even know where to start now...thanks for the advice...let me know if you find out or think of anything else.
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 06:08 PM   #8  
New Member
catrains is offline
 
Join Date: Jul 2008
Posts: 5
catrains See this member's comment history on his/her Profile page.
Quote:
Originally Posted by Missouri Bound
If you duplicated the wiring from the old to new, you probably did it correctly.
As for the breaker tripping, it's probably an issue with the water heater. Most water heaters fail with open elements, and some fail with the controls and allow both elements to come on at once....which is too high of a load for the breaker. Have the water heater checked.

Thanks for the reply...I will check the hot water heater..
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 06:49 PM   #9  
Electrical & Lighting Expert
Washington1 is offline
 
Join Date: Jun 2007
Posts: 680
Washington1 See this member's comment history on his/her Profile page.
I couldn't find a 64020Rs.

Do me a favor, and give me the name plate information. It should be located on your water heater.

Thanks!
  Reply With Quote
 
     
 
 
Old Jul 16, 2008, 07:31 PM   #10  
New Member
catrains is offline
 
Join Date: Jul 2008
Posts: 5
catrains See this member's comment history on his/her Profile page.
Quote:
Originally Posted by Washington1
I couldn't find a 64020Rs.

Do me a favor, and give me the name plate information. It should be located on your water heater.

Thanks!

Serial MO3505857
40 Gal
Model 640 20RS
4500 Watts
240 Volts
150 Working pressure

Trade Name Reliance
Reliance Water Heater Co.
Ashland, TN

That is it...i disconnected the hot water heater and the breaker does not trip...that proves it is the hotwater heater...also, the bottom heating element doesn't look good...i can't see the element, but the wires and such look burnt, especially the red one...we only replaced the top element...i will have to drain the tank and replace the element...what do i do about the burn wires....i would bet they run up in the tank...trace them?
  Reply With Quote
 
     


Thread Tools
Display Modes

 
Similar Sponsors

Similar Threads
Question Asker Forum Answers Last Post
Circuit breaker for my hot water heater keeps popping meljac0719 Plumbing 18 Jul 5, 2008 04:43 AM
Breaker keeps kicking out on water heater nascar2018 Plumbing 4 May 28, 2008 07:07 AM
water heater wiring into breaker panel usf67 Electrical & Lighting 3 Apr 26, 2008 07:14 PM
Hot water heater circuit breaker Cdaddy54 Plumbing 2 Feb 21, 2008 04:03 AM
Water Heater; Breaker Wiring? edgeX Electrical & Lighting 1 Dec 10, 2007 02:43 PM




Copyright ©2003 - 2007, Ask Me Help Desk.
All times are GMT -8. The time now is 02:17 PM.