I have a 15 amp 240 volt, ground fault circuit breaker (special order and pricey). I have this connected via 14/2 wire to a deep well pump submersed into the lake, and a 500 watt baseboard heater. This has been connected for 16 months with no problems. This weekend I could not get the circuit breaker to work without it tripping. I tried disconnecting the wires to the circuit breaker (no load) and it still tripped, I tried moving it to another location on the panel box still tripped. As a last resort I took out the gfi circuit breaker and connected a (on hand) 20 amp 240 volt circuit breaker. It did trip once but worked fine for the rest of the weekend (Saturday and Sunday). There has been record rainfall at the cottage the last couple of weeks and there have always been what appears to be voltage drops on the service as the lights will dim with no other loads (no motors or heavy voltage draws starting up when the lights dim.
Any ideas? I have checked the line at all locations looking for animal damage or obvious shorts (electrical boxes, box connectors, etc. No obvious shorts.

3 Answers
bhayne's Avatar
bhayne Posts: 341, Reputation: 79
Full Member
 
#2

Oct 23, 2006, 11:46 AM
This is not a faulty gfi. The more it rains the more conductive the ground becomes. I am surprised to see a well pump on a gfi. The long run will induce ground currents. The more conductive the ground is, the more easily current will flow until the gfi trips.

Most power supplies for water supply pumps do not require a gfi breaker. I would check local authorities to replace the gfi with a standard breaker and ground relay instead (if they want some indication of ground current).

The ground current is not a fault; it is normal behavior for this type of circuit.
Helpful
tkrussell's Avatar
tkrussell Posts: 9,673, Reputation: 3698
Senior Electrical & Lighting Expert
 
#3

Oct 23, 2006, 04:57 PM


I did not get that the circuit is long. The supply voltage is in question thou.

Voltage drop or sags will cause the current to raise slightly, and if left running long, may heat the breaker and trip due to an apparent overload.
And/or
The motor may not have the proper voltage to over come it's workload, and put the motor into a "locked rotor" condition, which can cause the amps to increase 6-10 times of running load.

The voltage drop may still exist and not getting better , but worsen due to a loose or corroded connection somewhere in the utility or home service equipment.

Or there is a ground fault, either in the motor due to a leak, or the heating element is wet or corroded. (I have to assume the heater is not in the lake with the motor).

Since the breaker still trips now with no load or wiring connected, indicates the GFI breaker is now probably defective.

The fact the standard breaker did trip indicates there still is a problem, but a standard breaker is not as sensitive to minor fluctuations,such as a GFI is.

The standard breaker must have overcome the fault or the fault is cleared enough to heat the unit up to eiminate any moisture inside.

The answer you received so far is inaccurate for your situation. If you are interested in reading a brief explanation how a 2 pole 240 volt GFI breaker works, see:

http://expert.ecmweb.com/resistance_...rcuit-breaker/
Helpful
bhayne's Avatar
bhayne Posts: 341, Reputation: 79
Full Member
 
#4

Oct 24, 2006, 07:14 AM
So, in simple you can replace the gfi with a 15A (or 20A if its 12/2 conductor which I suspect) 240V standard breaker as I have suggested, or

You can pull the pump, rebuild it, dig up the supply line and oversize all the conductors to compensate for voltage drop and buy another one of those 15A 240V GFI breakers.

Either way, your problem is solved!

You may also want to separate the baseboard heater on a different circuit to free up power to the pump. The pump deserves a dedicated supply (the tripping of the breaker may also be due to the cold days that now activate the 500W heater).
Helpful

Not your question? Ask your question View similar questions

 
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Add your answer here.

Remove Text Formatting

Undo
Redo
 
Decrease Size
Increase Size
Bold
Italic
Underline
Align Left
Align Center
Align Right
Ordered List
Unordered List
Decrease Indent
Increase Indent
Insert Email Link
Wrap [QUOTE] tags around selected text
Wrap [CODE] tags around selected text
Wrap [HTML] tags around selected text
Wrap [PHP] tags around selected text
Wrap [YOUTUBE] tags around selected text
Notification Type:



Check out some similar questions!

Circuit breaker [ 3 Answers ]

A circuit breaker connected to the kitchen tripped twice. I had an electrician in but the problem persists - in fact, the very day the electrician came. It does not seem to be caused by any one particular appliance. The first time I was using the waste disposal and the next two times nothing was...

Gfi breaker [ 1 Answers ]

I have an outdoor pond. I think that my electrical connection got wet and shorted out. My question is, I changed out all the receptacles on the gfi circuit and only two work. Is it possible that the breaker is bad and does not supply all of the circuits now?

GFI outlet vs girlfriend breaker [ 3 Answers ]

Is there a difference functionally between a GFI outlet and a GFI breaker? I am installing a jetted tub in the basement. The water pump has the two loose wires (+ground) and indicates the connection to be made in junction box and be protected by a GFI. A GFI for my type breaker is $300. I had...

Gfi circuit [ 1 Answers ]

I was wondering if when wiring for 2 gfis for different circuits, do I need separate neutrals for each or just a common one

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more Electrical & Lighting questions Search