| Russ,
A word about safety here. Please do not be fooled by the wire from the overhead to the switch. A switch ONLY carries load voltages, therefor both the black and the white wires are hot. (There should be a small wrap of black, red or blue tape around the white wire to signify that it is a load carrying wire not a neutral return. If there isn't any marking, put one there. It's for your safety.) In general, the overhead light will be on a 15 Amp Circuit. What is the amperage rating of the GFCI outlet that you want to install?
The reason I ask is if it is 20 Amp, then you may want to consider having an licensed electrician pull a permit, if required, and pull a 20 Amp line from the panel box to the where you want the GFCI.
Typically outlets and lights are on different circuits with power brought to the ceiling and a switch loop brings the load from the ceiling to the switch and then to the overhead light.
You may want to consult with an Electrical Inspector or a licensed electrician about whether or not you would be violating the NEC code if you pigtail the GFCI outlet to the 15 Amp source in the ceiling. |