2 Bathroom GFI Outlets and Vanity Light on same run
Hello,
I wanted to know if it's ok to run from my sub-panel from a 15 amp breaker a 12/3 over to a GFCI outlet , and then pigtail out 2 more runs from that GFCI outlet a 12/3 to another GFCI outlet and a 12/2 to the Vanity lights above.
On a 15 amp circuit you can use 14 gauge wire (which is easier to work with...and cheaper!).
Electrically, what you mention will work. You can also save a GFCI outlet, because any outlet downstream of the first GFCI will be protected if you hook it up to the "Load" or "Output" terminals. You'll probably want your vanity light to hook up to the "Line" or "Input" terminals. Here is a great diagram.
So guys thank you both for your answers, can you give me a quick run down of the wiring guage and if 12/3 is needed. Or can the whole run be on a 12/2. Basically, the subpanel is for the downstairs bathroom only, the run would have it's own dedicated 20 amp breaker. I would like to hook up 2 GFI's a vanity light and a bathroom fan on this run. Can you let me know how to wire this whole thing up. Thank you very much.
Also, you don't need to buy 2 separate gfci breakers. you can buy 1 and then a regular one that would be protected by it. If you're using a 20 amp breaker and 12 gauge wire you should go with 20 amp outlets. Otherwise if you buy a standard 15 amp outlet you could be running more than 15 amps in your outlet and you breaker won't trip because it's rated at 20 amps and your wire is also rated for 20 amps. If you were to run more than 15 amps through the outlet the circuit breaker in the panel would not trip and you could burn out your outlet. I'm rewording this answer for stanfortyman. It's just safest to go with 20 amps all the way around- I'm only telling you because I have had people come into the store where I worked and they had problems with burning out their outlets and the circuit breakers not tripping beforehand because they weren't consistent. I wasn't trying to get off topic but when someone mentioned 15 amp outlets I thought I should mention that it's not a good idea.
Also, you don't need to buy 2 separate gfci breakers. you can buy 1 and then a regular one that would be protected by it. If you're using a 20 amp breaker and 12 gauge wire you should go with 20 amp outlets. Otherwise if you buy a standard 15 amp outlet you could be running more than 15 amps in your outlet and you breaker won't trip because it's rated at 20 amps and your wire is also rated for 20 amps. This will cause you to fry your outlet and who knows what else if that were to happen
Sorry bud (or Sis), this is all wrong.
The rating of the receptacle has NOTHING to do with it when you are talking about 15 and 20A circuits.
A 15A receptacle, GFI or not, CAN certainly carry 20A. They are all rated for 20A feed-through. It will NOT "fry".
Look at a 15A rated GFI receptacle. It says right on it "20A feed-through" or something to that effect.
Also, a GFI receptacle has NO overcurrent built in, it is NOT a "breaker". Meaning it does NOT trip if you draw too much. This is a function of the circuit breaker.
that's exactly it. the outlet doesn't trip, so when you use a 15 amp outlet and you have 12 gauge wire behind the wall and a 20 amp outlet everything is rated for 20 amp except the outlet, and if for some reason you have too much current going through the outlet the 20 amp breaker in the panel will not trip. All I'm saying is that its safer to be consistent. I didn't say anything about the gfi having a breaker in it.
Guys we're getting off topic here, i really just need to know how to run the wire 12/2? 12/3? from my sub panel to a GFI from that GFI to another GFI also powering a Vanity Light through a switch and a toilet fan through a switch. Thank you
There are people here that will answer your question direct and to the point. I think i know the answer but i am not qualified and therefore not confident enough to do so.
for clarification for the others you are looking to have a 20 amp breaker feed 2 GFCI protected outlets and a single switch to a vanity light and fan correct?
lmangileri, you have NO clue what you are talking about and you are out of your league here.
Much as I really don't care about those red and green boxes, it was quite adolescent for you to give me a negative rating (in retaliation) when my information is ACCURATE.
I am done with you with regard to that, but I WILL correct any inaccuracies I see.
Quote:
Originally Posted by lmangileri
that's exactly it. the outlet doesn't trip, so when you use a 15 amp outlet and you have 12 gauge wire behind the wall and a 20 amp outlet everything is rated for 20 amp except the outlet, and if for some reason you have too much current going through the outlet the 20 amp breaker in the panel will not trip.(WHAT?!?!?!?!?) All I'm saying is that its safer to be consistent. I didn't say anything about the gfi having a breaker in it.
COMPLETELY inaccurate.
A GFI has NOTHING to do with overcurrent. NOTHING!
Like I said, 15A receptacles ARE rated for 20A feed-through.
-- Sorry everyone else, posters like this make me crazy, especially when they try to justify their blatantly incorrect advice.