I have ran a 1 1/4 inch conduit a distance of 75 feet to a sub-panel. What size awg thhn wire should I use to connect to it? Our ambient temp is 75 F.

1 Answer
tkrussell's Avatar
tkrussell Posts: 9,673, Reputation: 3698
Senior Electrical & Lighting Expert
 
#2

Mar 2, 2010, 12:24 PM


3- #3 copper or #1 aluminum. You will also need one # 8 CU or a #6 Al for equipment ground.
.
Helpful

Not your question? Ask your question View similar questions

 
Thread Tools Search this Thread
Search this Thread:

Advanced Search

Add your answer here.

Remove Text Formatting

Undo
Redo
 
Decrease Size
Increase Size
Bold
Italic
Underline
Align Left
Align Center
Align Right
Ordered List
Unordered List
Decrease Indent
Increase Indent
Insert Email Link
Wrap [QUOTE] tags around selected text
Wrap [CODE] tags around selected text
Wrap [HTML] tags around selected text
Wrap [PHP] tags around selected text
Wrap [YOUTUBE] tags around selected text
Notification Type:



Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 14 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Condo/Apt. New 100 amp service - BX wire size? [ 12 Answers ]

Hi All! I currently have an old 40 amp service in my pre-war condo. We are allowed to run BX securely attached for a new service. The distance is 250 feet. I am looking to get a 100 amp service. What size BX cable should be used for this? Do they make BX large enough for a 250 foot 100 amp...

Design ambient temp & evaporating temp? [ 1 Answers ]

If a manufacturer says their compressor can be used in a 2-1/2 ton compressor when the design ambient temperature is 100 F and the evaporating temperature is 45 F how do I measure/verify these temps for my location? Is the design ambient temp the outdoor temperature? Is the evaporating temp the...

WHAT WOULD BE The best size AWG to use for an 80 and 100 amp service [ 2 Answers ]

This in reference to a regular size commercial run

Wire service, wire gauge 100 amp [ 1 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...


View more Electrical Engineering questions Search