    Basement Flooding
    Just moved into a 100 year old home in New England, I had an alarm installed with a "flood" option... The alarm went off one early morning and I went downstairs to check the problem and found the basement was covered in two inches of water thanks to Spring thaw and a good deal of rain. It all subsided and evaporated within 2 days. The water was bubbling up through the floor, and I assume it was ground water pressure that caused the flooding. Even though the whole thing self corrected, I'm pretty sure I need to take some sort of action.

    Initially, I thought I'd have French drains installed, but that doesn't make sense to me because if the water has enough pressure to bubble through the concrete, it surely would overrun the drains.

    Based upon my research, it looks like my only viable option is to install a sump basin and pump. Is this a correct conclusion?

    If I am correct and a sump is the solution, is the location of the sump important? How do you determine where to position it? It's a large basement shold I install 2 sumps?

    Are there any "how to" web references on building a sump?

    Thanks in advance for your help..

    Lou I.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    May 1, 2005, 08:26 PM
    How much slope does your lot have? Gravity is more reliable than a sump pump. Is it feasible to start at the lowest side of the basement and run a drain out to a slope or ditch? You need to be able to slope the drain down all the way, but reach a point within reason where the drain can freely empty. Bust up a corner of the basement floor and hope it has a good gravel bed under it so the water can flow to the drain. Run the drain through or under the footer or wall and out to the open drain.

    Also make sure the ground slopes away from the house all the way around. If not, you may have to cut swales, wide, shallow ditches on the high side running to the low side to keep water away from the foundation.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    May 2, 2005, 05:39 AM
    Quote Originally Posted by loueye
    Just moved into a 100 year old home in New England, I had an alarm installed with a "flood" option... The alarm went off one early morning and I went downstairs to check the problem and found the basement was covered in two inches of water thanks to Spring thaw and a good deal of rain. It all subsided and evaporated within 2 days. The water was bubbling up through the floor, and I assume it was ground water pressure that caused the flooding. Even though the whole thing self corrected, I'm pretty sure I need to take some sort of action.

    Initially, I thought I'd have French drains installed, but that doesn't make sense to me because if the water has enough pressure to bubble through the concrete, it surely would overrun the drains.

    Based upon my research, it looks like my only viable option is to install a sump basin and pump. Is this a correct conclusion?



    If I am correct and a sump is the solution, is the location of the sump important? How do you determine where to position it? It's a large basement shold I install 2 sumps?

    Are there any "how to" web references on building a sump?

    Thanks in advance for your help..

    Lou I.
    Hey Lou,

    Lab man was totally correct when he said that gravity was the best and the cheapest way to go. However sometimes sump pumps are the only way to keep your basement dry. Let me give a few detail;s about sump pumps and if you decide you wish to learn how to build your own we can explore it further. Cheers, Tom
    --------------------------------------------------------------------------------

    Coping With Floods
    Information For Dealing With Floods

    --------------------------------------------------------------------------------

    Sump Pump Questions
    Thomas Scherer, Extension Agricultural Engineer




    For many homeowners the first line of defense against water in the basement is a sump with a pump in it. The sump may be connected to drain tile that drains the footings of the house, under the entire basement, or just the area where the sump is located. Many houses have tiling installed only around a portion of the house. The water that drains into the sump must be removed, and this is accomplished with a sump pump.

    The two basic sump pump models are the up-right (commonly called a pedestal) and the submersible. Either will work well with proper maintenance.

    The pedestal pump has the motor on top of the pedestal and the pump at the base, which sits on the bottom of the sump. The motor is not meant to get wet. The pump is turned on and off by a ball float. One advantage of this type of pump is that the on/off switch is visible so the action of the ball float can be easily seen.

    Submersible pumps are designed to be submerged in water and sit on the bottom of the sump. The on/off switch is attached to the pump and can be either a ball float connected to an internal pressure switch or a sealed, adjustable, mercury-activated float switch. The sealed mercury switch is generally more reliable than the pressure switch.

    Either type of pump should have a check valve on the water outlet pipe so water doesn't flow back in the sump when the pump shuts off. Water flowing back and forth can cause the pump to turn on and off more frequently than necessary and decrease the life of the pump.





    Some frequently asked questions about sump pumps:
    Q. How do you check or test a sump pump?
    A. First, make sure the outlet pipe is not frozen shut or plugged and that it directs water away from the house. Next make sure the pump is plugged in. Remove the lid (if the sump has one) and use a flashlight to check if the sump is clean and that the pump inlet is not plugged. Then slowly pour about 5 gallons of water into the sump. Try to simulate the speed that water would normally flow into the sump. Watch the action of the on/off switch and listen to the pump. Make the pump turn on and off at least twice. If something doesn't work right, fix it as soon as possible.

    Q. Can you burn the pump out if the outdoor pipe is frozen shut, or will it automatically shut off?
    A. Most pumps will not burn up, but they can overheat if left in this condition. Almost all sump pump motors have thermal protection built in. If they do overheat you just have to shut them off and let them cool down. The thermal relay will reset.

    Q. What size pump should I have for my house?
    A. There is no "correct" size. The horsepower requirement for a house is determined by the area of drainage connected to the sump, the depth to groundwater, the depth of the basement, and many other factors. A 1/3 hp pump is satisfactory for most houses.

    Q. Are there any problems with replacing a 1/3 hp pump with a 1/2 hp pump?
    A. When used in similar conditions, a 1/2 hp pump will pump more water and lift it higher than a 1/3 hp pump. Most new sump pumps will have a chart or graph in the instructions or on the box that shows the flow versus height of lift for both sizes. The flow is usually given in either gallons per minute or gallons per hour (multiply gpm by 60 to convert to gph). The height of lift is given in feet of vertical lift. There shouldn't be any problem, but where the flow into the sump is relatively slow there would be no advantage to using the larger pump. However, in situations where water flow can become rapid, a 1/2 hp pump may be able to keep up with the flow where a 1/3 hp pump may not.

    Q. Do sump pumps have filters which need to be cleaned or replaced?
    A. Sump pumps do not have filters, but they do have screens or small openings where the water enters the pump. These can sometimes be plugged.

    Q. Can or should you pump into a sewer drain or basement floor drain?
    A. No, you should not. If you have a septic system, under no circumstances should the sump be pumped into the basement floor drain. During wet conditions the drainfield of the septic system is usually saturated and struggling to handle the normal flow of water from the house. Adding to it with a sump pump can damage the septic system. Even if you are connected to a public system the sump should not be pumped into a floor drain. Putting additional water into the sewer system can overload the public system, and there may be a regulation against pumping into it.

    Q. Where should the sump pump drain hose be run?
    A. Preferably, sump water should be discharged at least 20 feet away from the house in such a way that it drains away from the house. It should not be directed onto a neighbor's lot, into window wells, or onto a septic system drainfield.

    Q. Can the average person replace a defective sump pump or does it require specialized tools or the expertise of a plumber?
    A. Almost all sump pumps come with a list of required tools and directions for installation. It should not be difficult for the "average" person to replace a sump pump.

    Q. How big should the sump hole be? What kind of hole liner should you use? How much gravel do you put under and around it?
    A. Sump holes should be about 2 feet in diameter. This allows space for the pump and associated piping and to store water between pumping events (about 15 to 25 gallons). Metal or plastic liners can be used, but plastic is easier to work with and it the material of choice. When the sump liner is installed, about 3 to 4 inches of coarse gravel should be placed in the bottom of the hole. The gravel forms a solid base for the pump as well as helping to prevent mud and other debris from clogging the pump.

    Q. Should the sump pump be on an isolated electrical circuit?
    A. A standard 15-amp, three-prong grounded outlet is sufficient to handle a sump pump. A sump pump is always in or near water, so it is best to have an outlet with a ground fault interrupter (GFI).

    Q. I don't have a sump in my basement but am concerned about water leaking in. What can I do?
    A. You can push the water to the floor drain, but if water backs up in the floor drain or drains very slowly a pump is needed. Small pumps sometimes referred to as "skimmer" pumps are designed to sit on a flat surface and pump when water on the floor is only 1/4 to 1/2 inch deep. They can often be used with a common garden hose. A 50-foot garden hose run out through a basement window will usually carry the water far enough away from the house. You can remove more water by taking the cover off the floor drain and placing the pump in the drain bowl -- these pumps are usually small enough to fit in the bowl. In emergencies where electric service is off, these pumps can be powered by a small gasoline generator.
    loueye's Avatar
    loueye Posts: 3, Reputation: 1
    New Member
     
    #4

    May 2, 2005, 10:53 AM
    Thanks.

    I guess I misunderstood the role of a sump.

    I thought a sump offered the "path of least resistance" to water attempting to force it's way through concrete. I thought that water would collect in the sump and follow the concrete to the sump, and when it rose to a high enough level the pump would engage and evacuate the water.

    It sounds like, based upon your description, that a sump acts as a collection point after the water enters the basement, more like a drain than an alternate path.

    I rather not have the water in the basement at all, so I'll take a look at other measures.

    Thanks again.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Toilet flooding hot water, sewer stink? [ 15 Answers ]

Old (1962) slab house, southwest Florida. Half-bath off bedroom. A couple days of toilet gurgling, a couple back-ups, but no overflowing, and plunging worked. Then it wouldn't, but it would eventually run down empty and kind of breathe out that nasty sewer smell from time to time. I thought...

Minor basement flooding [ 2 Answers ]

Tonight we had a very bad rainstorm, and my basement window which is one of those below ground ones, allowed for some water to seep into my home. It basically hugged the walls and then puddled onto my carpeted basement room. I noticed it pretty quickly so was able to move furniture and electrical...

Help My Home is Flooding [ 5 Answers ]

Every time it rains a lot we have water that seaps in to our sunken den under our hearth and under our back door. At times this can be a lot of water. We have put french drains in but have NOT been able to stop this water. I don't even know who to speak with. Can anybody give me a idea of at...

Wet bar in basement [ 3 Answers ]

Hi, I want to put in a wet bar (sink) in my basement, but I don't know where to drain the sink. As I explained in a previous post. "I want to put a sink in my basement, but I dont know where to drain it. Basicaly I have three pipes in my cement floor and I don't know what they are for....

91 civic with stalling/flooding [ 17 Answers ]

(this was posted on a previous 91 civic problem thread... these problems sound different, so I posed a new question.. sorry about the double post) Hi all, Im a new owner of a 91 civic w/ 146k miles... the first two weeks I drove it, it worked fine. Then the problems... It would start to...


View more questions Search