    Nov 20, 2005, 11:02 PM
    Air condition will not shut off
    My thermostat [the older kind] has seemed as if it was showing the wrong temps [showing warmer than it felt]. Now the air blowing out doesn't feel as cold as it was. When I switch to off it blows warm air. I can only shut if off through circuit breaker and that feels warm to the touch. The fan is in the auto mode. I live in a mobil home in Florida. Also, it doesn't seem to have the water dripping out if its pipe outside like it always does. :confused: Any ideas! I can read directions fine but do not know about testing strengths and such. Thanks for any help.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Nov 21, 2005, 07:28 AM
    Let the system run for 5-10 minutes. Go out to the outside unit. In addition to the fan running, there should be sort of a put, put, put of the compressor. If it is running, the larger tube coming out to it should be cool and the small one warm or hot. If so, there is little you can do except call a service man. It is is not running at all, a wire may be damaged or the relay bad.

    I came across the niftiest gadget for trouble shooting, a voltage detector. They work through the insulation of wires. There are several brands. I have a GB Instruments GVD-505A, less than $15 at Home Depot. Touch it to a hot wire, and the end glows red. Find the doodad that lights it on one side, and not the other, and you have the culprit.

    Check the small wires coming from the thermostat with a voltmeter or voltage detector. They should have 24 volts AC. If not, go inside and check at the furnace. The Y and B or C terminals should have the same wires connected to them as outside and again 24 volts AC. If they have power inside, but not outside, the wires are damaged. If they don't have power, either the wires are damaged from the thermostat, or it is bad.
    skiberger's Avatar
    skiberger Posts: 562, Reputation: 41
    Senior Member
     
    #3

    Nov 21, 2005, 12:12 PM
    If your getting warmer air the system may be low on refrigerant. May be a leak somewhere in lines. When was the last time the inside & outside coils, filter, blower fan & thermostat were cleaned?
    Susyn's Avatar
    Susyn Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 21, 2005, 03:12 PM
    I only have access to outside water heater and outside air conditioning unit with heater package, but not to any furnace. I have found some receipts from previous owner and this 2 1/2 ton unit was installed in '87 and last serviced in '91! So, skiberger, I think its time to call the big boys in. :eek: It could be very simple thing but... Anyway thanks for help and ideas. I'm still open to any thoughts as I won't be able to get a serviceman right away.
    Also, Labman, I will be getting a voltage detector, thanks for info.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane Air Condition circuit breakers trips [ 7 Answers ]

I have a Trane Air Condition that refuses to run more that 10 minutes without tripping the circuit breaker when tempertures are below 32 degs. I read that at low tempertures, more features are needed to keep the heat up. Operation of these features seems to overload the circuit. There must be a...

Scalp Condition: What is it? [ 2 Answers ]

I have flaky, dandruff-like skin and I've always assumed it was just dandruff. The past few months, however, it seemed like more than just dandruff. I have researched it, and cannot find exactly what it might be. My scalp is very oily and I have oily skin. I get patches on my scalp that are very...

Pre-existing condition [ 1 Answers ]

My husband was laid off his job in Feb. 2006. His insurance continued through the end of Feb. and then I added him to my insurance as of March 1st 2006. His doctor scheduled an endoscopie. It was done in May(under MY insurance). Because he had talked with his doctor about acid reflux in Jan. and...

Air condition [ 3 Answers ]

OK I live in a mobile home in Oklahoma its been 100 pluse here last couple weeks and I noticed the other day my unit way making a scretching sound everyonece in a while then today it was a long scretching that didn't stop so I felt the air vent and it was blowing hot air so turned the unit off......

Is my window ac is going to work in this condition? [ 4 Answers ]

I live on the fifth floor of an apartment.I want to install a window ac(0.8 ton) in my bedroom(11"x10") .For installation of an AC,our builder has provided an opening in the wall.My problem is that ,the guy leaving next to me (on fifth floor) has installed AC and exhaust of his AC directly faces to...


View more questions Search