May 2, 2010, 07:04 PM
|
|
How many deep freezers can run off one 15A circuit?
I have an upright deep freezer that is standard fridge size and a chest style freezer that is 50 in wide and want to run them off the same 15 A circuit, would this be a problem?
{threads merged}
|
|
|
Uber Member
|
|
May 2, 2010, 07:06 PM
|
|
Personally I would have each on its own breaker, with both compressors kicking in at the same time, may trip breaker.
|
|
|
Home Repair & Remodeling Expert
|
|
May 2, 2010, 07:50 PM
|
|
I agree. You should tell us the current requirements for each to be sure but 2 units on one 15amp will likely blow.
|
|
|
New Member
|
|
May 4, 2010, 08:47 AM
|
|
THanks guys but I only have one circuit remaining to run both and I've read that when the compressor kicks in, it only draws 2-3 amps. Do either of you know if this is true?
|
|
|
New Member
|
|
May 4, 2010, 08:49 AM
|
|
How many deep freezers can run off one 15A circuit?
I have an upright deep freezer that is standard fridge size and a chest style freezer that is 50 in wide and want to run them off the same 15 A circuit, would this be a problem?
|
|
|
Home Repair & Remodeling Expert
|
|
May 4, 2010, 08:55 AM
|
|
Yes, a post 1986 freezer could use 2-3 amps when running but double that on start up. Can you tell us what's on the tags of both freezers in either watts or amps required?
|
|
|
Home Repair & Remodeling Expert
|
|
May 4, 2010, 08:57 AM
|
|
Why the new post, we are the same guys here as yesterday. Tell us the wattage or amps required for both freezers. On start up they each could pull up to 10 amps.
|
|
|
Uber Member
|
|
May 4, 2010, 02:02 PM
|
|
I suggest that you read and follow the manufacturers instructions for each unit. I suspect that both will state that each requires a separate circuit.
Chances are for both to start at the same time is very low. Take the chance and ignore the advice of having both on separate circuits, all may be fine for who knows how long, till one day they both happen to start at the same time, and the breaker will trip.
Then you can take the advice and put each on it's own circuit.
|
|
|
Uber Member
|
|
May 4, 2010, 06:21 PM
|
|
If the wiring is in conduit, you can pull extra wires and use a double breaker(not to be confused with a 2 pole breaker).
2 breakers in the space of 1.
|
|
|
New Member
|
|
May 4, 2010, 07:19 PM
|
|
The one freezer says 4 amps, the other is sitting in a friend's garage waiting to be picked up, it's a year old and about the same size as the 4 amp which is about 12 years old. Assuming it's 4 amps or less, is it safe to say it should work off one circuit?
|
|
|
Home Repair & Remodeling Expert
|
|
May 4, 2010, 07:24 PM
|
|
Nope, not yet, 4 amps is running amps and we are guessing about the other one. $ amps running could ba as much as 8 staring amp. If they were identical then they could blow a 15 amp breaker if they kicj in at the same time. TK mentioned earlier that both at once would be a very slight chance but it would eventually happen. If you were not in the area to notice the breaker blew you lose. Is you wire in conduit or is it cable or BX?
|
|
|
New Member
|
|
May 6, 2010, 06:31 PM
|
|
So one is 4 amps and the other is 3 amps, will this work?
|
|
|
Uber Member
|
|
May 6, 2010, 09:39 PM
|
|
Do you ever have power outages where you live?
It MAY work for many years like that, can you tell us if it is in conduit or not?
I would have on separate if possible, One could develop a problem and cause the breaker to blow, losing food to 2 freezers.
|
|
|
New Member
|
|
May 7, 2010, 07:16 PM
|
|
Occasional power outages, not sure on the conduit. How do you tell?
|
|
|
Home Repair & Remodeling Expert
|
|
May 7, 2010, 07:26 PM
|
|
Conduit is a grayish steel pipe in which the wires are run. If you have several wires that are encased in PVC you have cable that
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Increasing from 15A circuit to 20A
[ 4 Answers ]
Need your expertise,
My living room and my bed room are on the same circuit breaker and they are under 15A load.
Lately, I have more devices that connect to the receptacles in the living room, such as:
Denon AVR-4308
XBox360
48 LCD TV
Wii
500W HTPC
15A receptacles on 12/2 GFCI Circuit
[ 5 Answers ]
I was just looking at some of the wiring that was done in my house when it was built in 2003. I have one GFCI Circuit that has 5 receptacles on it. On this, it is wired all with 12/2 to the garage first, where the receptacle is the GFI, then it runs 3 outdoor receptacles, and 1 in the basement. ...
Square D 15A Circuit Breaker
[ 1 Answers ]
In my home, I have a Square D service panel. I am changing one of the circuit breakers from a standard breaker to a GFCI type (the circuit is outside). I could not find any 15A Square D breakers at any of my local stores (Home Depot, Lowe's and a few electrical supply stores). Most stores carry...
How many lights on a 15A lighting circuit
[ 3 Answers ]
Hi everyone! First post and thanks in advance, hopefully!
I was wondering how many lights I can put on a 15A lighting circuit. I have a second floor that I want to put a (1) hall light, (3) closet lights, & (1) bedroom light. Would it be too much to put a bathroom vanity light and a vent...
View more questions
Search
|