Ask Experts Questions for FREE Help!
 

Free Answers in 3 Easy Steps

Register Now
3 Steps
 


Ask QuestionsprogressAnswer QuestionsprogressBuild ReputationprogressBecome an Expert
 
At Ask Me Help Desk you can ask questions in any topic and have them answered for free by our experts. To ask questions or participate in answering them you must register for a free account. By registering you will be able to:
  • Get free answers from experts in any of our 300+ topics.
  • Accept money for answers that you provide.
  • Communicate privately with other members (PM).
  • See fewer ads.
  Answer this Question    Ask about Heating & Air Conditioning    Ask about another Subject  
 

svpauhana
Oct 11, 2008, 08:12 AM
American Standard ASYSTAT655A conversion to White-Rogers 1F72-151 programable thermostat.

What are the correct terminlal connections?

hvac1000
Oct 11, 2008, 11:42 AM
Just in case you lost your instructions for your new thermostat here they are. This thermostat will only work for a two stage heat pump system or second stage gas/oil.


http://www.white-rodgers.com/wrdhom/pdfs/instruction_sheets/0037-6498.pdf


Your old thermostat subbase was made for American Standard/Trane/York by Honeywell company. Below is a link to the Honeywell site so you can see which wires were connected where and the color.

Note: easy does it on this conversion. if you happen to land the wrong wire on the wrong terminal that new thermostat of yours can go up in smoke. If you do not feel comfortable doing this conversion I recommend having a local HVAC company do your On site thermostat install.

On the right side of the page your terminal listing is FIGURE 10. This listing is for York but American Standard also used this.

http://customer.honeywell.com/techlit/pdf/69-0000s/69-0435.pdf







WIRE COLOR___FUNCTION____________OLD THERMO___NEW THERMO
white__________aux ht relay____________W_____________AUX
black__________outdoor thermistor_______T_____________? This wire not connected on new thermostat
green__________fan relay______________G_____________G
red____________transformer hot_________R_____________R w/jumper to Rc
brown__________outdoor thermostat______X2____________? This wire not connected on new thermostat
yellow_________compressor contactor____Y_____________Y
orange_________cool chg.over valve______O_____________O/B
blue___________transformer common_____B_____________C


I will mention this again. if you do not feel comfortable doing this change over let a professional ON Site HVAC person do the work.

Good luck.

svpauhana
Oct 13, 2008, 01:07 PM
Further ASYSTAT655A conversion to 1F72-151 questions:
The new stat doesn't have a AUX on the terminal blocks. Should I use the W2 terminal on E1 ?
Reference Rc - Is the jumper to be connected between R on E1 and C on E2 since there is no Rc ?

hvac1000
Oct 13, 2008, 01:42 PM
Yes W2 as stated in the W/R instructions.

No jumper at this time from RC.

I tried to find something close to the old unit but the diagram was not perfect.