The means for grounding a 200amp delta service enterance panal? The grounded and the grounding are on the same bus bar, ? Where should I ground my grounding rod & #6 bare grounding wire?
d_honga Aug 28, 2008, 10:57 AM The means for grounding a 200amp delta service enterance panal? The grounded and the grounding are on the same bus bar, ? Where should I ground my grounding rod & #6 bare grounding wire? thommyschnak Aug 28, 2008, 04:33 PM The #6 wire that is require for a 200A main service is to be bonded to the ground bar of this main panel, as well as the water ground which is required to be a #4 wire. In a main panel such as this all of the grounding is bonded together, just make sure that you have each wire in a sererate terminal. I you run out of space you may add additional grounding lugs, or bars, as long as your panel is made for this. I hope this helps! Sincerely, Tommy Schnak:cool: Copyright ©2005-, Ask Me Help Desk
|
||||||||