bigd53545
Oct 27, 2007, 10:08 AM
I have a Bryant furnace. The small draft inducer motor runs, but the blower doesn't come on. Any advice on this problem would be appreciated. Thank you.
bigd53545 Oct 27, 2007, 10:08 AM I have a Bryant furnace. The small draft inducer motor runs, but the blower doesn't come on. Any advice on this problem would be appreciated. Thank you. T-Top Oct 27, 2007, 05:47 PM If the inducer motor is running and its not trying to light you may have a restricted vent pipe or bad ignitor on the furnace. How old is the system? bigd53545 Oct 28, 2007, 08:25 AM The furnace was built in 1989. The main burner seems to be running at times. Are there a set of points that signal the blower to run after main burner is running? Thanks again for the help. esquire1 Oct 28, 2007, 09:07 AM Check the blower relay labman Oct 28, 2007, 10:08 AM Go to the sequence of operations of a gas furnace in http://www.askmehelpdesk.com/heating-air-conditioning/heating-cooling-maintenance-repair-troubleshooting-frequently-asked-questions-58313.html Your furnace is likely new enough that a timer on the circuit board operates a relay to start the blower. If it doesn't come on, a temperature sensor shuts the furnace down, and it tries to start again. Whether the timer or the relay is failing, likely you are out $$$$$$$$$$$$ to replace the board. Copyright ©2005-, Ask Me Help Desk
|
||||||||